Help! Can not get APCUPSD working
  • Help! Can not get APCUPSD working
    Hello, I've been trying to get this setup and i cant get past APCUPSD install, I have a cyberpower CP1500PFCLCD, It is connected to the HS3 Windows 10 Pc by USB, The devices and Printers in control panel shows the Battery icon and Hardware says its working, The UPS icon in the tray shows the battery at 100 percent. APCUPSD show ups unknown and host 127.0.0.1 port 3551. and the config is blank. I followed the install helps file but i can not find American power conversion USB UPS under Human interface devices? to install drivers. I have a section for batteries that shows HID UPS BATTERY but when i tried to update that one it gave the Error Code 10. so i hoping someone can give me an idea of what i missed so far??
  • #2
    What entries did you put in the apcupsd.conf file? Maybe post it here. Do you know if apcupsd works with that UPS? You may need to use NUT (https://networkupstools.org/) if the UPS is not compatible with the apcupsd daemon. The plugin supports both apcupsd and NUT.
    HS 3.0.0.532: 1963 Devices 1141 Events
    Z-Wave 3.0.1.261: 122 Nodes on one Z-Net
    • #3
      If you are using the USB setup, this may help
      I just setup apcupsd yesterday when I setup my new computer to run HomeSeer. On Windows 10 it can be a bit of a pain the way the USB driver needs to be setup.
      What worked for me was to follow the apcupsd driver installation instructions in \apcupsd\driver\install.txt to some degree...
      Loading in the driver using the apcupsd.inf file seemed to be the key.
      Billy Draper
      • #4
        ok, So it looks like this could be more than my basic skills can handle but im going to try and get this working if possible!!!
        bdraper i havent changed anything in my conf file, i thought it was not needed if it was a usb connection, i tried updating the driver under BATTERIES before and it gave me the error 10.. The install directions said this was the wrong device to update the drivers with.. My device manager only shows BATTERIES/HID UPS BATTERY, and the install says i should have American power conversion USB UPS under Human interface devices but that device is not there so im not sure how i can fix that or there is a dummy ups file for this like NUT has
        here is a copy of that file
        ## apcupsd.conf v1.1 ##
        # for apcupsd release 3.14.14 - win32-mingw
        # "apcupsd" POSIX config file
        # Note that the apcupsd daemon must be restarted in order for changes to
        # this configuration file to become active.
        # ========= General configuration parameters ============
        # UPSNAME xxx
        # Use this to give your UPS a name in log files and such. This
        # is particulary useful if you have multiple UPSes. This does not
        # set the EEPROM. It should be 8 characters or less.
        #UPSNAME
        # UPSCABLE <cable>
        # Defines the type of cable connecting the UPS to your computer.
        # Possible generic choices for <cable> are:
        # simple, smart, ether, usb
        # Or a specific cable model number may be used:
        # 940-0119A, 940-0127A, 940-0128A, 940-0020B,
        # 940-0020C, 940-0023A, 940-0024B, 940-0024C,
        # 940-1524C, 940-0024G, 940-0095A, 940-0095B,
        # 940-0095C, 940-0625A, M-04-02-2000
        UPSCABLE usb
        # To get apcupsd to work, in addition to defining the cable
        # above, you must also define a UPSTYPE, which corresponds to
        # the type of UPS you have (see the Description for more details).
        # You must also specify a DEVICE, sometimes referred to as a port.
        # For USB UPSes, please leave the DEVICE directive blank. For
        # other UPS types, you must specify an appropriate port or address.
        # UPSTYPE DEVICE Description
        # apcsmart COMx Newer serial character device, appropriate for
        # SmartUPS models using a serial cable (not USB).
        # Can be COM1, COM2, etc.
        # usb <BLANK> Most new UPSes are USB. A blank DEVICE
        # setting enables autodetection, which is
        # the best choice for most installations.
        # net hostnameort Network link to a master apcupsd through apcupsd's
        # Network Information Server. This is used if the
        # UPS powering your computer is connected to a
        # different computer for monitoring.
        # snmp hostnameort:vendor:community
        # SNMP network link to an SNMP-enabled UPS device.
        # Hostname is the ip address or hostname of the UPS
        # on the network. Vendor can be can be "APC" or
        # "APC_NOTRAP". "APC_NOTRAP" will disable SNMP trap
        # catching; you usually want "APC". Port is usually
        # 161. Community is usually "private".
        # netsnmp hostnameort:vendor:community
        # OBSOLETE
        # Same as SNMP above but requires use of the
        # net-snmp library. Unless you have a specific need
        # for this old driver, you should use 'snmp' instead.
        # dumb COMx Old serial character device for use with
        # simple-signaling UPSes. Can be COM1, COM2, etc.
        # pcnet ipaddr:usernameassphrase
        # PowerChute Network Shutdown protocol which can be
        # used as an alternative to SNMP with the AP9617
        # family of smart slot cards.ipaddr is the IP
        # address of the UPS mgmtcard. username and
        # passphrase are the credentials for which the card
        # has been configured.
        # modbus COMx Serial device for use with newest SmartUPS models
        # supporting the MODBUS protocol.
        # modbus <BLANK> Leave the DEVICE setting blank for MODBUS over USB
        # or set to the serial number of the UPS to ensure
        # that apcupsd binds to that particular unit
        # (helpful if you have more than one USB UPS).
        UPSTYPE usb
        DEVICE
        # POLLTIME <int>
        # Interval (in seconds) at which apcupsd polls the UPS for status. This
        # setting applies both to directly-attached UPSes (UPSTYPE apcsmart, usb,
        # dumb) and networked UPSes (UPSTYPE net, snmp). Lowering this setting
        # will improve apcupsd's responsiveness to certain events at the cost of
        # higher CPU utilization. The default of 60 is appropriate for most
        # situations.
        #POLLTIME 60
        # SCRIPTDIR <path to script directory>
        # Directory in which apccontrol and event scripts are located.
        SCRIPTDIR c:\apcupsd\etc\apcupsd
        # PWRFAILDIR <path to powerfail directory>
        # Directory in which to write the powerfail flag file. This file
        # is created when apcupsd initiates a system shutdown and is
        # checked in the OS halt scripts to determine if a killpower
        # (turning off UPS output power) is required.
        PWRFAILDIR c:\apcupsd\etc\apcupsd
        # NOLOGINDIR <path to nologin directory>
        # Directory in which to write the nologin file. The existence
        # of this flag file tells the OS to disallow new logins.
        NOLOGINDIR c:\apcupsd\etc\apcupsd
        # ======== Configuration parameters used during power failures ==========
        # The ONBATTERYDELAY is the time in seconds from when a power failure
        # is detected until we react to it with an onbattery event.
        # This means that, apccontrol will be called with the powerout argument
        # immediately when a power failure is detected. However, the
        # onbattery argument is passed to apccontrol only after the
        # ONBATTERYDELAY time. If you don't want to be annoyed by short
        # powerfailures, make sure that apccontrol powerout does nothing
        # i.e. comment out the wall.
        ONBATTERYDELAY 6
        # Note: BATTERYLEVEL, MINUTES, and TIMEOUT work in conjunction, so
        # the first that occurs will cause the initation of a shutdown.
        # If during a power failure, the remaining battery percentage
        # (as reported by the UPS) is below or equal to BATTERYLEVEL,
        # apcupsd will initiate a system shutdown.
        BATTERYLEVEL 5
        # If during a power failure, the remaining runtime in minutes
        # (as calculated internally by the UPS) is below or equal to MINUTES,
        # apcupsd, will initiate a system shutdown.
        MINUTES 3
        # If during a power failure, the UPS has run on batteries for TIMEOUT
        # many seconds or longer, apcupsd will initiate a system shutdown.
        # A value of 0 disables this timer.
        # Note, if you have a Smart UPS, you will most likely want to disable
        # this timer by setting it to zero. That way, you UPS will continue
        # on batteries until either the % charge remaing drops to or below BATTERYLEVEL,
        # or the remaining battery runtime drops to or below MINUTES. Of course,
        # if you are testing, setting this to 60 causes a quick system shutdown
        # if you pull the power plug.
        # If you have an older dumb UPS, you will want to set this to less than
        # the time you know you can run on batteries.
        TIMEOUT 0
        # Time in seconds between annoying users to signoff prior to
        # system shutdown. 0 disables.
        ANNOY 300
        # Initial delay after power failure before warning users to get
        # off the system.
        ANNOYDELAY 60
        # The condition which determines when users are prevented from
        # logging in during a power failure.
        # NOLOGON <string> [ disable | timeout | percent | minutes | always ]
        NOLOGON disable
        # If KILLDELAY is non-zero, apcupsd will continue running after a
        # shutdown has been requested, and after the specified time in
        # seconds attempt to kill the power. This is for use on systems
        # where apcupsd cannot regain control after a shutdown.
        # KILLDELAY <seconds> 0 disables
        KILLDELAY 0
        # ==== Configuration statements for Network Information Server ====
        # NETSERVER [ on | off ] on enables, off disables the network
        # information server. If netstatus is on, a network information
        # server process will be started for serving the STATUS and
        # EVENT data over the network (used by CGI programs).
        NETSERVER on
        # NISIP <dotted notation ip address>
        # IP address on which NIS server will listen for incoming connections.
        # This is useful if your server is multi-homed (has more than one
        # network interface and IP address). Default value is 0.0.0.0 which
        # means any incoming request will be serviced. Alternatively, you can
        # configure this setting to any specific IP address of your server and
        # NIS will listen for connections only on that interface. Use the
        # loopback address (127.0.0.1) to accept connections only from the
        # local machine.
        NISIP 0.0.0.0
        # NISPORT <port> default is 3551 as registered with the IANA
        # port to use for sending STATUS and EVENTS data over the network.
        # It is not used unless NETSERVER is on. If you change this port,
        # you will need to change the corresponding value in the cgi directory
        # and rebuild the cgi programs.
        NISPORT 3551
        # If you want the last few EVENTS to be available over the network
        # by the network information server, you must define an EVENTSFILE.
        EVENTSFILE c:\apcupsd\etc\apcupsd\apcupsd.events
        # EVENTSFILEMAX <kilobytes>
        # By default, the size of the EVENTSFILE will be not be allowed to exceed
        # 10 kilobytes. When the file grows beyond this limit, older EVENTS will
        # be removed from the beginning of the file (first in first out). The
        # parameter EVENTSFILEMAX can be set to a different kilobyte value, or set
        # to zero to allow the EVENTSFILE to grow without limit.
        EVENTSFILEMAX 10
        # ========== Configuration statements used if sharing =============
        # a UPS with more than one machine
        # Remaining items are for ShareUPS (APC expansion card) ONLY
        # UPSCLASS [ standalone | shareslave | sharemaster ]
        # Normally standalone unless you share an UPS using an APC ShareUPS
        # card.
        UPSCLASS standalone
        # UPSMODE [ disable | share ]
        # Normally disable unless you share an UPS using an APC ShareUPS card.
        UPSMODE disable
        # ===== Configuration statements to control apcupsd system logging ========
        # Time interval in seconds between writing the STATUS file; 0 disables
        STATTIME 0
        # Location of STATUS file (written to only if STATTIME is non-zero)
        STATFILE c:\apcupsd\etc\apcupsd\apcupsd.status
        # LOGSTATS [ on | off ] on enables, off disables
        # Note! This generates a lot of output, so if
        # you turn this on, be sure that the
        # file defined in syslog.conf for LOG_NOTICE is a named pipe.
        # You probably do not want this on.
        LOGSTATS off
        # Time interval in seconds between writing the DATA records to
        # the log file. 0 disables.
        DATATIME 0
        # FACILITY defines the logging facility (class) for logging to syslog.
        # If not specified, it defaults to "daemon". This is useful
        # if you want to separate the data logged by apcupsd from other
        # programs.
        #FACILITY DAEMON
        # ========== Configuration statements used in updating the UPS EPROM =========
        # These statements are used only by apctest when choosing "Set EEPROM with conf
        # file values" from the EEPROM menu. THESE STATEMENTS HAVE NO EFFECT ON APCUPSD.
        # UPS name, max 8 characters
        #UPSNAME UPS_IDEN
        # Battery date - 8 characters
        #BATTDATE mm/dd/yy
        # Sensitivity to line voltage quality (H cause faster transfer to batteries)
        # SENSITIVITY H M L (default = H)
        #SENSITIVITY H
        # UPS delay after power return (seconds)
        # WAKEUP 000 060 180 300 (default = 0)
        #WAKEUP 60
        # UPS Grace period after request to power off (seconds)
        # SLEEP 020 180 300 600 (default = 20)
        #SLEEP 180
        # Low line voltage causing transfer to batteries
        # The permitted values depend on your model as defined by last letter
        # of FIRMWARE or APCMODEL. Some representative values are:
        # D 106 103 100 097
        # M 177 172 168 182
        # A 092 090 088 086
        # I 208 204 200 196 (default = 0 => not valid)
        #LOTRANSFER 208
        # High line voltage causing transfer to batteries
        # D 127 130 133 136
        # M 229 234 239 224
        # A 108 110 112 114
        # I 253 257 261 265 (default = 0 => not valid)
        #HITRANSFER 253
        # Battery charge needed to restore power
        # RETURNCHARGE 00 15 50 90 (default = 15)
        #RETURNCHARGE 15
        # Alarm delay
        # 0 = zero delay after pwr fail, T = power fail + 30 sec, L = low battery, N = never
        # BEEPSTATE 0 T L N (default = 0)
        #BEEPSTATE T
        # Low battery warning delay in minutes
        # LOWBATT 02 05 07 10 (default = 02)
        #LOWBATT 2
        # UPS Output voltage when running on batteries
        # D 115
        # M 208
        # A 100
        # I 230 240 220 225 (default = 0 => not valid)
        #OUTPUTVOLTS 230
        # Self test interval in hours 336=2 weeks, 168=1 week, ON=at power on
        # SELFTEST 336 168 ON OFF (default = 336)
        #SELFTEST 336
        after some google searching i found a post in another forum that also confirmed what sparkman asked and said APCUPSD is not compatible and to use Nut. so I dloaded Nut and installed it, it detected a unknown ups but didnt give any errors, i started the service and changed HS3 plugin to 127.0.0.1 port 3493 but nothing showed up. i did some more google searching and found some info on NUT that said i needed to use dummy-ups but im not sure what needs to be done with the file "Cyber_Power_Systems__CP1500PFCLCD__usbhid-ups__2.7.1__01.dev" , i am looking through the help files but everything seems to gear towards linux not windows 10
        page with info from NUT with DEV file to use
        https://networkupstools.org/ddl/Cybe...500PFCLCD.html
        • #5
          I tried to setup the .conf file for nut to get the dummy device to work but still nothing, BLUPS auto detected everything i need for now so i will use it until i can figure out how to get NUT working with my cyber-power CP1500PFCLCD
          Thanks for the help, once NUT is working I know everything will work