My energy meter is only reporting positive values. When I set the parameter to report negative and positive then all values go to zero. I have solar so I should see power flow in both directions. Each time I set parameter2 to value one as Aeon suggest then Homeseer reports 0 for Watts and Kwh. Is anyone else getting negative and positive power flows? How?
I have an Aeotec Aeon Home Energy Meter (HEM) Gen5 ZW095. (It has positive and negative reporting capabilities)
If I set parameter 2 to a value of zero (0) it works but only positive absolute values
If I set parameter 2 to a value of one (1) nothing works, all values go zero.
Parameter Manual: https://s3.amazonaws.com/cdn.freshde...lication%2Fpdf
For Parameter 2 in the HEM Root
Default Value = 0 (If I change this to anything else it reports zero values)
Parameter Value options (Size 1)
0 = report power, energy absolute value;
1 = report positive/negative power, report the algebraic sum energy;
2 = report positive/negative power, only report energy positive part (consuming electricity);
3 = report positive/negative power, only report energy negative part (generating electricity)
I have an Aeotec Aeon Home Energy Meter (HEM) Gen5 ZW095. (It has positive and negative reporting capabilities)
If I set parameter 2 to a value of zero (0) it works but only positive absolute values
If I set parameter 2 to a value of one (1) nothing works, all values go zero.
Parameter Manual: https://s3.amazonaws.com/cdn.freshde...lication%2Fpdf
For Parameter 2 in the HEM Root
Default Value = 0 (If I change this to anything else it reports zero values)
Parameter Value options (Size 1)
0 = report power, energy absolute value;
1 = report positive/negative power, report the algebraic sum energy;
2 = report positive/negative power, only report energy positive part (consuming electricity);
3 = report positive/negative power, only report energy negative part (generating electricity)