    Honeywell TH8320ZW scheduling issue please help

    I have a Honeywell TH8320ZW thermostat installed. It functions fine as a device, meaning i can change the set points and control all function on HS3. i just can't however get it to change the temperature set point when running an event to schedule.

    Here is my event...

    IF The time is at 7:00:00 AM
    Then
    Set Device Node 20 Z-Wave Heating Setpoint to 65 F
    Then
    Set Device Node 20 Z-Wave Fan Mode to Circulation



    Here is the log showing that the event triggered - note that the fan mode changed but not the heating set point
    Feb-26 7:01:58 AM Z-Wave Device: Node 20 Z-Wave Fan State Set to Fan State 0
    Feb-26 7:00:00 AM Z-Wave Device: Node 20 Z-Wave Fan State Set to Fan State 1
    Feb-26 7:00:00 AM Z-Wave Device: Node 20 Z-Wave Fan Mode Set to 6
    Feb-26 7:00:00 AM Device Control Device: Node 20 Z-Wave Fan Mode to Circulation (6)
    Feb-26 7:00:00 AM Event Event Trigger "Thermostat PLAYROOM HEAT HOME"

    Here are the device pages for heating set point device
    Reference ID 93
    Technology Address 003D7F62-020-Q29
    Status 65 = Dim
    Value 65 = "65 F"
    String
    Supports Status True
    Dimmable False
    Interface Z-Wave
    Extra Data Store 39 Named entries, 0 UnNamed entries.
    Device Type Internal Thermostat API, Type: Thermostat Setpoint, SubType: Heating 1
    Device Type (String)
    Misc Settings Show Values, Generate Voice Command, SET_DOES_NOT_CHANGE_LAST_CHANGE
    Device Image File images\Devices\Image-Not-Selected.png
    Thumbnail Image File images\Devices\Image-Not-Selected_small.png
    Relationship Status Child
    Associated Devices Node 20 Z-Wave Thermostat
    Scale Display Text F
    Information About Node 20
    Options
    Polling Interval: 0 Hours 0 Minutes 0 Seconds Edit Time Span
    Functions
    Test Connectivity Optimize Full Optimize Audit This Node
    Settings
    Associations




    Here is the requested info to paste at the bottom of the page

    MESSAGE BOARD (copy/paste section below to message board posts)

    Current Date/Time: 2/26/2019 9:08:19 AM
    HomeSeer Version: HS3 Pro Edition 3.0.0.500
    Operating System: Microsoft Windows Embedded Standard - Work Station
    System Uptime: 1 Day 13 Hours 38 Minutes 33 Seconds
    IP Address: 10.0.0.37
    Number of Devices: 88
    Number of Events: 27
    Available Threads: 200
    HSTouch Enabled: True
    Event Threads: 0
    Event Trigger Eval Queue: 0
    Event Trigger Priority Eval Queue: 0
    Device Exec Queue: 0
    HSTouch Event Queue: 0
    Email Send Queue: 0
    Anti Virus Installed:
    In Virtual Machine: No MFG: shuttle inc.
    Enabled Plug-Ins
    3.0.21.28949: Blue-Iris
    3.0.0.33: EnvisaLink
    3.0.1.87: Z-Wave


    Any help would be appreciated.
    Thanks,
    Sal

    #2
    Is it taking almost two minutes to change that setting? If so something is wrong with the Z-Wave communications. Do you have a lot of Z-Wave devices? You may also want to update your Z-Wave plugin to the latest release and test again.
    💁‍♂️ Support & Customer Service 🙋‍♂️ Sales Questions 🛒 Shop HomeSeer Products

    Comment


      #3
      I have two of those thermostats and I have no trouble changing the setpoints. Are you running it with the builtin schedule by chance? You can't do that and have HS control of setpoints. I've never used the builtin scheduling.

      Comment


        #4
        I just upgraded my z-wave plugin. I will see if it runs tonight. thank you.

        I am not using the built in schedule

        Comment


          #5
          I updated my zwave plugin and i am still having the same issue
          the event triggers. the fan child device responds to the event but not the heat set point child device
          IF The time is at 3:00:00 PM
          Then
          Set Device Node 20 Z-Wave Heating Setpoint to 55
          Then
          Set Device Node 20 Z-Wave Fan Mode to Auto
          event log
          Feb-26 3:00:00 PM Z-Wave Device: Node 20 Z-Wave Fan Mode Set to 0
          Feb-26 3:00:00 PM Device Control Device: Node 20 Z-Wave Fan Mode to Auto (0)
          Feb-26 3:00:00 PM Event Event Trigger "Thermostat PLAYROOM HEAT AWAY"

          Comment


            #6
            Mine match what you have shown for the device advance tab, other than I have 15 minute polling set for the set points. This is what I have under the Z-wave node information for one of them.

            Full Name: HVAC Hall Thermostat Polling: Polling Disabled
            Manufacturer:
            Honeywell
            Type:
            0x11
            ID:
            0x1
            Listens:
            Yes
            Version: 2.97 (ZDK 4.51) Firmware: 1.1 Neighbor Count:
            6
            Speed:
            40Kbps
            Neighbors: 1, 3, 7, 15, 16, 17
            Uses Interface: Zstick (May change next Optimize) Basic Type: ROUTING SLAVE, Generic Type: THERMOSTAT, Specific Type: THERMOSTAT GENERAL V2
            Command Classes:
            Supported: Association, Setpoint(V 2), Mode(V 2), Basic, Fan State(V 1), Operating State(V 1), Fan Mode(V 3), Switch All, Sensor Multilevel(V 3), Manufacturer Specific, Version
            Child Device: Temperature CC: Sensor Multilevel Ver: 3 Polling: Polling Disabled
            Child Device: Fan Mode CC: Fan Mode Ver: 3 Polling: Polling Disabled
            Child Device: Fan State CC: Fan State Polling: Polling Disabled
            Child Device: Mode CC: Mode Ver: 2 Polling: Polling Disabled
            Child Device: Operating State CC: Operating State Polling: Polling Disabled
            Child Device: Heating Setpoint CC: Setpoint Ver: 2 Polling: Polling Interval: 15m, 0s
            Child Device: Cooling Setpoint CC: Setpoint Ver: 2 Polling: Polling Interval: 15m, 0s
            An event to set one:

            IF HVAC HVAC Temperature Set Period changes and becomes Away

            AND IF The Group Conditions are all TRUE


            Then
            Set Devices HVAC Den Heating Setpoint to 65 F
            HVAC Hall Heating Setpoint to 65 F
            HVAC Den Cooling Setpoint to 80 F
            HVAC Hall Cooling Setpoint to 82 F

            Comment


              #7
              JOEGR are you in heating mode or AUTO mode?
              I was able to get the setpoint to change through the event if i first gave it a "set mode to heat" command just before the heating setpoint command

              Comment


                #8
                Sorry, I didn't think about that. I am always in heating or cooling mode, never auto. (I have events that use outside temperature as well as inside temperature and last run time to decide to switch between heat and cool.) Note that you can set both the heating and the cooling set-points in either heat or cool mode.

                Comment