    Originally posted by rmasonjr View Post
    A device is orphaned when it is deleted from HS. If you delete it from within the plugin, the device is automatically removed.
    > My case, the device was not deleted from HS, rather the linkage between the plugin and HS device was lost/corrupted somehow and the plugin defaulted to "OFF" relative to a device it no longer has a map to.
    I honestly believe the disconnect issues you are having is causing the other symptoms you are seeing. Once we get it stable, the plugin runs great.
    > I agree! But maybe we're using the term"disconnect" differently. I don't believe the plug "disconnected" the Zee was always online, only one occasion I saw the panel go offline. I think disconnect now means the plugin mapping to the HS device.
    Question: If I had a backup file with all the correct linkages (the most current after any changes) would it be simply a matter of reloading the backup configuration file?
      #47
      The plugin is having problems linking the OMNI devices to the HS devices due to the network issues you're having. I've had no other reports of HS devices losing that linkage to an OMNI device.
      It's possible that a backup config file will restore the HS devices, but until things are stable, I wouldnt go to the trouble.
      HS4Pro on a Raspberry Pi4
      54 Z-Wave Nodes / 21 Zigbee Devices / 108 Events / 767 Devices
      Plugins: Z-Wave / Zigbee Plus / EasyTrigger / AK Weather / OMNI
      HSTouch Clients: 1 Android
        #48
        I just requested a button push using Alexa and it showed up as pushed in the Homeseer web control but the Omni never got the request. This happens once or twice a week. To fix I have to go to the HS web control site and navigate to Tools, then System then request a Restart System. After about 5 min. all is working well again for 3 or 4 days. Then the Omni again fails to get the HS request.
        RapRap is this like your problem?
          #49
          Correct, this is the symptom.
            #50
            Can you post your logs so I can take a look?
            What I'm looking for is if the plugin was disconnected or if there were some error either sending/receiving from the panel.
              #51
              I suspect that when I updated HS to HS3 ZEE S2 Edition 3.0.0.475 last night is the reason I get zilch when going to Omni Plug Ins, then Omni, then Omni Logs, then Load Logs. This Log thing has always been confusing to me. Or do I go to View, then Logs which give me a time line type log and here that is pasted. It also starts anew after the HS edition update and since then I haven't experienced a disconnect as I wrote about. Need a few days. BTW is the following log what you are looking for Mason?
              Oct-19 12:21:16 PM Info Latest BETA update available is: 3.0.0.478
              Oct-19 12:21:16 PM Info Latest update available is: 3.0.0.475
              Oct-19 12:21:16 PM Info Checking for updates...
              Oct-19 10:15:00 AM Log Info The log database is currently 0.05MB in size.
              Oct-19 9:06:00 AM Energy DB Info All energy database compacting routines completed.
              Oct-19 9:06:00 AM Energy DB Info No Records. Vacuuming database to condense.
              Oct-19 9:06:00 AM Energy DB Info Energy database compaction initiated.
              Oct-19 7:15:00 AM Log Info The log database is currently 0.05MB in size.
              Oct-19 5:06:00 AM Energy DB Info All energy database compacting routines completed.
              Oct-19 5:06:00 AM Energy DB Info No Records. Vacuuming database to condense.
              Oct-19 5:06:00 AM Energy DB Info Energy database compaction initiated.
              Oct-19 4:15:00 AM Log Info The log database is currently 0.05MB in size.
              Oct-19 1:15:00 AM Log Info The log database is currently 0.05MB in size.
              Oct-19 1:06:00 AM Energy DB Info All energy database compacting routines completed.
              Oct-19 1:06:00 AM Energy DB Info No Records. Vacuuming database to condense.
              Oct-19 1:06:00 AM Energy DB Info Energy database compaction initiated.
              Oct-18 11:43:40 PM OMNI ---------------------------
              Oct-18 11:43:40 PM OMNI Plugin startup is complete.
              Oct-18 11:43:40 PM OMNI Synchronization complete.
              Oct-18 11:31:57 PM OMNI Synchronizing OMNI devices with HomeSeer...
              Oct-18 11:31:56 PM OMNI Requesting initial system troubles
              Oct-18 11:31:48 PM OMNI Requesting Output status...
              Oct-18 11:31:42 PM OMNI Requesting Area status...
              Oct-18 11:31:42 PM OMNI All configuration and properties retrieved.
              Oct-18 11:31:40 PM OMNI -->Reading properties...
              Oct-18 11:31:39 PM Web Server Web Server authorized local login successful from: 192.168.1.235 User: chasers03@gmail.com
              Oct-18 11:30:29 PM OMNI Reading panel configuration...
              Oct-18 11:30:22 PM Startup Start up complete.
              Oct-18 11:30:22 PM Info Processing updates completed.
              Oct-18 11:30:22 PM Info System connected to MyHS Service successfully with license ID 94468.
              Oct-18 11:30:22 PM Info Latest BETA update available is: 3.0.0.478
              Oct-18 11:30:22 PM Info System connected to MyHS Service, waiting for acknowledge...
              Oct-18 11:30:22 PM Info Latest update available is: 3.0.0.475
              Oct-18 11:30:22 PM TTS Speak ():Welcome to Home-Seer
              Oct-18 11:30:22 PM Startup Scripting is OK and is now running Startup.vb
              Oct-18 11:30:22 PM Info Checking for updates...
              Oct-18 11:30:22 PM Startup HSSentry is disabled in Setup, sentry will not be started.
              Oct-18 11:30:22 PM Startup Starting Event Scheduler...
              Oct-18 11:30:01 PM Starting Plug-In Plugin OMNI started successfully in 2367 milliseconds
              Oct-18 11:29:59 PM Startup Running the startup script Startup.vb
              Oct-18 11:29:59 PM Startup Starting Find service...
              Oct-18 11:29:59 PM Startup Updater services starting...
              Oct-18 11:29:58 PM Starting Plug-In Initializing plugin OMNI ...
              Oct-18 11:29:58 PM Info Plugin OMNI has connected. IP:127.0.0.1:43550
              Oct-18 11:29:58 PM Database Opening (Mode=Read/Write) up HomeSeer Energy database /usr/local/HomeSeer/Data/Energy/Energy.hsd
              Oct-18 11:29:58 PM Speech Listening for remote speaker connections on port 10401
              Oct-18 11:29:58 PM Startup Initializing Speaker Client Interface
              Oct-18 11:29:58 PM Startup Start automation engine...
              Oct-18 11:29:57 PM Web Server Web Server started on port 80
              Oct-18 11:29:57 PM Web Server Local IP address is: 192.168.1.80
              Oct-18 11:29:57 PM Startup HStouch server started, waiting for clients to connect.
              Oct-18 11:29:57 PM HSTouch Server Server started on port 10200
              Oct-18 11:29:57 PM Plug-In Finished initializing plug-in OMNI
              Oct-18 11:29:57 PM Startup Initializing Plug-Ins
              Oct-18 11:29:57 PM Plug-In Found plug-in: Z-Wave, version: 3.0.1.77
              Oct-18 11:29:56 PM Plug-In Found plug-in: OMNI, version: 3.0.2.17
              Oct-18 11:29:55 PM Startup Checking for available plug-ins
              Oct-18 11:29:55 PM Info Remote plug-in API interface started on port 10400
              Oct-18 11:29:55 PM Startup This version of HomeSeer is registered as a HS3ZEES2 version.
              Oct-18 11:29:55 PM Startup Creating Speaker Client Interface Object...
              Oct-18 11:29:55 PM Startup HomeSeer version is: 3.0.0.475
              Oct-18 11:29:55 PM Load Config Loading TIMERS...
              Oct-18 11:29:55 PM Load Config Loading COUNTERS...
              Oct-18 11:29:55 PM Load Config 18 total events loaded.
              Oct-18 11:29:55 PM Load Config Loading Events...
              Oct-18 11:29:55 PM Load Config Loading Event Groups...
              Oct-18 11:29:55 PM Load Config 225 total devices loaded.
              Oct-18 11:29:54 PM Database Loading Devices...
              Oct-18 11:29:53 PM Database Opening (Mode=Read/Write) up HomeSeer LOG database /tmp/HomeSeerLog.hsd
              Oct-18 11:29:53 PM Database Opening (Mode=Read Only) up HomeSeer database /usr/local/HomeSeer/Data/Latest Homeseer Data.hsd
              Oct-18 11:29:53 PM Startup Loading configuration file ...
              Oct-18 11:29:53 PM Startup Database SAVE process started.
              Oct-18 11:29:53 PM Startup Local voice recognition class started.
              Oct-18 11:29:53 PM Startup Plug-In Interface class started.
              Oct-18 11:29:53 PM Startup E-Mail RECEIVE class started.
              Oct-18 11:29:53 PM Startup E-Mail SEND class started.
              Oct-18 11:29:53 PM Startup Web server class started.
              Oct-18 11:29:53 PM Startup Application interface class started.
              Oct-18 11:29:53 PM Startup COM port classes started.
              Oct-18 11:29:53 PM Startup Creating Class Objects...
              Oct-18 11:29:53 PM Startup ************************************************************ ********************
              Oct-18 11:29:53 PM Startup HomeSeer version 3.0.0.475 Edition: HS3 ZEE S2 Starting Now
              Oct-18 11:29:52 PM Startup Settings Loaded.
                #52
                I've been experiencing these random disconnects, plugin crashing, and whatnot for about a month now. It all happened when I updated the plugin to the latest version, more that a month ago. Up until then everything was pretty stable. Now the plugin just randomly hangs, has panel connection issues, and sometimes gets into a state, where zones are working fine but outputs are not. Sometimes, it's stable for a week, then stops working, and goes without issues, sometimes, it's only 1 day, for me it's random. Here is a preview form today, when the outputs stopped working, and I had to restart homeseer.
                10/18/2018 11:30:03 PM [2]  [SECURE]
                10/18/2018 11:30:03 PM [2]  [--> Zone 105 changed status.  Updating Homeseer...]
                10/18/2018 11:30:07 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:07 PM [2]  [---->Zone]
                10/18/2018 11:30:07 PM [2]  [ZONE:  zone=[]  number=[105]  status=[NOT READY]]
                10/18/2018 11:30:07 PM [2]  [Zone [105]  status=[1]  [1]]
                10/18/2018 11:30:07 PM [2]  [MapZoneStatus_V2: zoneId=[105] status=[1] zoneChanged=[False] annotation=[(EE4-9)] statusText=[NOT READY] zoneType=[64] zoneTypeText=[Auxiliary] name=[Mount Wall PIR] area=[2] analogLoop=[250] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[10/18/2018 11:30:07 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[699] hsParentRef=[6] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0]  highsetpoint=[0]]
                10/18/2018 11:30:07 PM [2]  [NOT READY]
                10/18/2018 11:30:07 PM [2]  [--> Zone 105 changed status.  Updating Homeseer...]
                10/18/2018 11:30:07 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:30:07 PM [2]  [---->Unit]
                10/18/2018 11:30:07 PM [2]  [-->UNIT:  desc=[]  number=[434]  name=[MtnBdrn Ocpd]]
                10/18/2018 11:30:07 PM [2]  [-->Unsolicited: Unit=[434]  status=[1]/[ON FOR 0:45:00]]
                10/18/2018 11:30:07 PM [2]  [-->Unsolicited: raising event for flag 434]
                10/18/2018 11:30:07 PM [2]  [--> Flag 434 changed status.  Updating Homeseer...]
                10/18/2018 11:30:09 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:09 PM [2]  [---->Zone]
                10/18/2018 11:30:09 PM [2]  [ZONE:  zone=[]  number=[105]  status=[SECURE]]
                10/18/2018 11:30:09 PM [2]  [Zone [105]  status=[0]  [0]]
                10/18/2018 11:30:09 PM [2]  [MapZoneStatus_V2: zoneId=[105] status=[0] zoneChanged=[False] annotation=[(EE4-9)] statusText=[SECURE] zoneType=[64] zoneTypeText=[Auxiliary] name=[Mount Wall PIR] area=[2] analogLoop=[250] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[10/18/2018 11:30:09 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[699] hsParentRef=[6] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[SECURE] hsZoneStatus=[2] lowSetpoint=[0]  highsetpoint=[0]]
                10/18/2018 11:30:09 PM [2]  [SECURE]
                10/18/2018 11:30:09 PM [2]  [--> Zone 105 changed status.  Updating Homeseer...]
                10/18/2018 11:30:13 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:15 PM [2]  [---->Auxillary]
                10/18/2018 11:30:17 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:30:21 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:21 PM [2]  [---->Auxillary]
                10/18/2018 11:30:28 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:30:41 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:30:45 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:45 PM [2]  [---->Unit]
                10/18/2018 11:30:45 PM [2]  [-->UNIT:  desc=[]  number=[437]  name=[Mstr2 Ocupd]]
                10/18/2018 11:30:45 PM [2]  [-->Unsolicited: Unit=[437]  status=[0]/[0]]
                10/18/2018 11:30:45 PM [2]  [-->Unsolicited: raising event for flag 437]
                10/18/2018 11:30:45 PM [2]  [--> Flag 437 changed status.  Updating Homeseer...]
                10/18/2018 11:30:53 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:30:53 PM [2]  [---->Auxillary]
                10/18/2018 11:30:56 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:31:11 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:31:21 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:31:21 PM [2]  [---->Auxillary]
                10/18/2018 11:31:26 PM [2]  [CONNECTION STATUS: Retrying]
                10/18/2018 11:31:35 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/18/2018 11:31:35 PM [2]  [---->Zone]
                10/18/2018 11:31:35 PM [2]  [ZONE:  zone=[]  number=[98]  status=[NOT READY]]
                10/18/2018 11:31:35 PM [2]  [Zone [98]  status=[1]  [1]]
                10/18/2018 11:31:35 PM [2]  [MapZoneStatus_V2: zoneId=[98] status=[1] zoneChanged=[False] annotation=[(EE4-2)] statusText=[NOT READY] zoneType=[64] zoneTypeText=[Auxiliary] name=[Ocean Ceil PIR] area=[2] analogLoop=[145] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[10/18/2018 11:31:35 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[693] hsParentRef=[6] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0]  highsetpoint=[0]]
                10/18/2018 11:31:35 PM [2]  [NOT READY]
                10/18/2018 11:31:35 PM [2]  [--> Zone 98 changed status.  Updating Homeseer...]
                10/18/2018 11:31:35 PM [2]  [---->Unit]
                10/18/2018 11:31:35 PM [2]  [-->UNIT:  desc=[]  number=[435]  name=[OcnBdrn Ocpd]]
                10/18/2018 11:31:35 PM [2]  [-->Unsolicited: Unit=[435]  status=[1]/[ON FOR 0:44:59]]
                10/18/2018 11:31:35 PM [2]  [-->Unsolicited: raising event for flag 435]
                10/18/2018 11:31:35 PM [2]  [--> Flag 435 changed status.  Updating Homeseer...]
                10/18/2018 11:31:41 PM [2]  [CONNECTION STATUS: No Reply]
                10/18/2018 11:31:41 PM [2]  [CONNECTION STATUS: Disconnected]
                10/18/2018 11:31:41 PM [2]  [CONNECTION STATUS: Interrupted Function Call]
                10/19/2018 6:53:36 AM [2]  [SetIOMulti: CC.Ref=[573]  CC.ControlValue=[0]]
                10/19/2018 6:53:37 AM [2]  [PressButton: 20]
                10/19/2018 6:53:37 AM [2]  [SetIOMulti: CC.Ref=[278]  CC.ControlValue=[0]]
                10/19/2018 6:53:37 AM [2]  [Output_Off: outp=271 length=1 duration=0 d=0]
                10/19/2018 6:53:37 AM [2]  [SetIOMulti: CC.Ref=[248]  CC.ControlValue=[0]]
                10/19/2018 6:53:37 AM [2]  [Output_Off: outp=392 length=1 duration=0 d=0]
                10/19/2018 6:53:41 AM [2]  [SetIOMulti: CC.Ref=[249]  CC.ControlValue=[0]]
                10/19/2018 6:53:41 AM [2]  [Output_Off: outp=257 length=1 duration=0 d=0]
                10/19/2018 6:53:44 AM [2]  [SetIOMulti: CC.Ref=[250]  CC.ControlValue=[0]]
                10/19/2018 6:53:44 AM [2]  [Output_Off: outp=258 length=1 duration=0 d=0]
                10/19/2018 7:06:56 AM [2]  [SetIOMulti: CC.Ref=[850]  CC.ControlValue=[1]]
                10/19/2018 7:06:56 AM [2]  [Output_On: outp=391 length=1 duration=0 d=0]
                10/19/2018 7:06:56 AM [2]  [SetIOMulti: CC.Ref=[293]  CC.ControlValue=[1]]
                10/19/2018 7:06:56 AM [2]  [Output_On: outp=390 length=1 duration=0 d=0]
                10/19/2018 7:07:13 AM [2]  [SetIOMulti: CC.Ref=[850]  CC.ControlValue=[1]]
                10/19/2018 7:07:13 AM [2]  [Output_On: outp=391 length=1 duration=0 d=0]
                10/19/2018 7:07:13 AM [2]  [SetIOMulti: CC.Ref=[293]  CC.ControlValue=[0]]
                10/19/2018 7:07:13 AM [2]  [Output_Off: outp=390 length=1 duration=0 d=0]
                here is one where the plugin crashed.
                10/8/2018 1:04:44 PM [2]  [SECURE]
                10/8/2018 1:04:44 PM [2]  [--> Zone 42 changed status.  Updating Homeseer...]
                10/8/2018 1:04:44 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/8/2018 1:04:44 PM [2]  [---->Auxillary]
                10/8/2018 1:04:44 PM [2]  [Temperature Zone 26 changed status. Reading=[76.0]]
                10/8/2018 1:04:44 PM [2]  [Zone [26]  Temperature-->76]
                10/8/2018 1:04:44 PM [2]  [Temperature Zone 27 changed status. Reading=[79.0]]
                10/8/2018 1:04:44 PM [2]  [Zone [27]  Temperature-->79]
                10/8/2018 1:05:02 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/8/2018 1:05:02 PM [2]  [---->Auxillary]
                10/8/2018 1:05:02 PM [2]  [Temperature Zone 65 changed status. Reading=[75.0]]
                10/8/2018 1:05:02 PM [2]  [Zone [65]  Temperature-->75]
                10/8/2018 1:05:04 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/8/2018 1:05:04 PM [2]  [---->Zone]
                10/8/2018 1:05:04 PM [2]  [ZONE:  zone=[]  number=[42]  status=[NOT READY]]
                10/8/2018 1:05:04 PM [2]  [Zone [42]  status=[1]  [1]]
                10/8/2018 1:05:04 PM [2]  [MapZoneStatus_V2: zoneId=[42] status=[1] zoneChanged=[False] annotation=[(EX2-10)] statusText=[NOT READY] zoneType=[64] zoneTypeText=[Auxiliary] name=[CPIR Dining Rm] area=[2] analogLoop=[249] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[10/8/2018 1:05:04 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[655] hsParentRef=[6] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0]  highsetpoint=[0]]
                10/8/2018 1:05:04 PM [2]  [NOT READY]
                10/8/2018 1:05:04 PM [2]  [--> Zone 42 changed status.  Updating Homeseer...]
                10/8/2018 1:05:09 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/8/2018 1:05:09 PM [2]  [---->Zone]
                10/8/2018 1:05:09 PM [2]  [ZONE:  zone=[]  number=[117]  status=[NOT READY]]
                10/8/2018 1:05:09 PM [2]  [Zone [117]  status=[1]  [1]]
                10/8/2018 1:05:09 PM [2]  [MapZoneStatus_V2: zoneId=[117] status=[1] zoneChanged=[False] annotation=[(EE5-5)] statusText=[NOT READY] zoneType=[64] zoneTypeText=[Auxiliary] name=[DinRmCeilingPIR] area=[2] analogLoop=[147] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[10/8/2018 1:05:09 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[1054] hsParentRef=[6] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0]  highsetpoint=[0]]
                10/8/2018 1:05:09 PM [2]  [NOT READY]
                10/8/2018 1:05:09 PM [2]  [--> Zone 117 changed status.  Updating Homeseer...]
                10/8/2018 1:05:09 PM [2]  [---->Unit]
                10/8/2018 1:05:09 PM [2]  [-->UNIT:  desc=[]  number=[453]  name=[DiningRmOccp]]
                10/8/2018 1:05:09 PM [2]  [-->Unsolicited: Unit=[453]  status=[1]/[ON FOR 0:30:00]]
                10/8/2018 1:05:09 PM [2]  [-->Unsolicited: raising event for flag 453]
                10/8/2018 1:05:09 PM [2]  [--> Flag 453 changed status.  Updating Homeseer...]
                10/8/2018 1:05:13 PM [2]  [UNSOLICITED: ExtendedStatus]
                10/8/2018 1:05:13 PM [2]  [---->Auxillary]
                10/8/2018 1:05:14 PM [2]  [Temperature Zone 27 changed status. Reading=[78.0]]
                10/8/2018 1:05:14 PM [2]  [Zone [27]  Temperature-->78]
                10/8/2018 1:05:22 PM [2]  [UNSOLICITED: SystemEvents]
                10/8/2018 1:05:22 PM [2]  [CONNECTION STATUS: Unexpected Error]
                10/8/2018 1:05:43 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:05:48 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:05:55 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:06:04 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:06:15 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:06:28 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:06:43 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:06:58 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:07:13 PM [2]  [CONNECTION STATUS: Retrying]
                10/8/2018 1:07:28 PM [2]  [CONNECTION STATUS: No Reply]
                10/8/2018 1:07:28 PM [2]  [CONNECTION STATUS: Disconnected]
                10/8/2018 4:11:59 PM [2]  [SetIOMulti: CC.Ref=[568]  CC.ControlValue=[0]]
                10/8/2018 4:11:59 PM [2]  [PressButton: 12]
                10/8/2018 4:12:20 PM [2]  [SetIOMulti: CC.Ref=[569]  CC.ControlValue=[0]]
                10/8/2018 4:12:20 PM [2]  [PressButton: 13]
                10/8/2018 4:12:58 PM [2]  [SetIOMulti: CC.Ref=[850]  CC.ControlValue=[1]]
                10/8/2018 4:12:58 PM [2]  [Output_On: outp=391 length=1 duration=0 d=0]
                10/8/2018 4:12:58 PM [2]  [SetIOMulti: CC.Ref=[293]  CC.ControlValue=[0]]
                10/8/2018 4:12:58 PM [2]  [Output_Off: outp=390 length=1 duration=0 d=0]
                10/8/2018 4:13:01 PM [2]  [SetIOMulti: CC.Ref=[850]  CC.ControlValue=[1]]
                10/8/2018 4:13:01 PM [2]  [Output_On: outp=391 length=1 duration=0 d=0]
                10/8/2018 4:13:01 PM [2]  [SetIOMulti: CC.Ref=[293]  CC.ControlValue=[1]]
                10/8/2018 4:13:01 PM [2]  [Output_On: outp=390 length=1 duration=0 d=0]
                I will be sending the full logs later today via email to rmasonjr, but in the mean time let me know if there is any other info you need
                  #53
                  No, those are the HomeSeer logs. Hover over Plugins -> OMNI -> OMNI Logs
                  you'll need to make sure you have logging set to DEBUG first...
                    #54
                    Thanks - at first glance, there was some network interruption. Those CONNECTION STATUS entries come from the HAI SDK, so I need to see what would cause something like that to happen.
                      #55
                      Update on the HS-Omni here. It has been 24+ hours since I discovered the HS-OMNI device dissociations. Since correcting all thoses, the system has been rock solid.
                      I also re-linked the Google Home account and that is working flawlessly. Re-syncing Google Home is hit and miss.
                      This morning ~6AM the Zee rebooted. I don't know why. Power glitch? In any case, after the reboot the Zee log show a myriad of errors related to Zwave and Zwave devices. The database seemed to be mucked up but the system was running. HS support suggested resetting the Zwave interface which I did. Logs are all quiet now and all is working.
                      What happened? I don't know, I suspect the Zee database became corrupted.
                      Watching the system carefully now..
                      I bought the HS Zee for two reasons: i) OMNI interface, and ii) Google Home integration.
                        #56
                        It could be a power supply issue with the Zee. If you have a spare one, or even a spare USB charger, try it for a while and see. Do you have a UPS?
                          #57
                          Try also to disable HSSentry (Software system monitor) from running.
                          I have seen the ZWave plugin and utilization take down Homeseer 3 before.
                          Disconnects or corrupted DB's would cause grief with my HS3Pro / lite set up.
                          The RPi3 does also utilize more power than the RPi2 such that you do need a better power supply for it.
                          Many folks also add heat sinks to the device.
                          - Pete
                          Auto mator
                          HS4 Pro - Ubuntu 22.04 / Lenova Tiny M900 / 32Gb Ram
                            #58
                            Good info Pete and rmasonjr , thank you.
                            As of right now, still rock solid. All the logs are perfectly quiet. The fact the the Omni-HS database appeared to be mucked up followed by a flush of zwave device database errors is strong circumstantial evidence.
                            I have the original Zee power supply and it's plugged into a UPS with surge protection. Are you saying Pete that the power supply could be a bit too underpowered?
                            I do have some power supplies kicking around and I will swap it out at the first sign of issues returning.
                            Zee is located in an equipment closet that used to house a whole bunch of A/V gear which is no longer does. But, the closet is well ventilated and temperature monitored. It typically runs ~80 degrees plus/minus. Highest I have seen is upper 80s. Checking with an IR thermometer the Zee seems to run 10 - 15 degrees above room temperature.
                              #59
                              This is a Posting test only to see why I am not getting notifications by email of posts to this subscribed forum. Sorry for the bother from Chasers. Still trying to troubleshoot my disconnects which I sense sometimes are caused by the gateway wifi going down. Wouldn't you think that if the Omni reengages then shouldn't the Z2 after a wifi interruption. On second thought these devices are Ethernet not wireless????
                                #60
                                I've been watching this thread with interest as I have an OmniPro II with the HS3 plugin, and I'm seeing panel disconnects frequently.
                                In my case, the Omni panel is isolated from my network using Pete's microrouter suggestion. The HS3 box is a dedicated Minix box, nothing else running there, but I do have plenty of IP cameras on the same Ethernet segment, so I do see about 25% utilization of the network.
                                My HS3 installation is at my vacation home, nothing fancy, just monitors a Cartell driveway sensor and sends an email when a vehicle is detected. Also have a TEMP08 with some 1-wire temperature sensors to view temperature trends, and a BlueIris plugin for my camera server. Some X10 and some ZWave, nothing more.
                                Omni log:
                                2018-10-23 9:09:48 PM [2] [CONNECTION STATUS: Disconnected]
                                2018-10-23 9:09:48 PM [2] [CONNECTION STATUS: Retrying]
                                2018-10-23 9:09:43 PM [2] [CONNECTION STATUS: Connection Timed Out]
                                2018-10-23 9:09:39 PM [2] [CONNECTION STATUS: Retrying]
                                2018-10-23 9:09:32 PM [2] [CONNECTION STATUS: Retrying]
                                2018-10-23 9:09:27 PM [2] [CONNECTION STATUS: Retrying]
                                2018-10-23 9:09:19 PM [2] [--> Zone 9 changed status. Updating Homeseer...]
                                2018-10-23 9:09:19 PM [2] [TRIPPED]
                                2018-10-23 9:09:19 PM [2] [MapZoneStatus_V2: zoneId=[9] status=[20] zoneChanged=[False] annotation=[Z9] statusText=[TRIPPED] zoneType=[3] zoneTypeText=[AwayInt] name=[Hall Motion] area=[1] analogLoop=[148] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[2018-10-23 9:09:19 PM] isSecurityZone=[True] isArmingZone=[True] hsDeviceRef=[3254] hsParentRef=[3234] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[SECURE] hsZoneStatus=[2] lowSetpoint=[0] highsetpoint=[0]]
                                2018-10-23 9:09:19 PM [2] [Zone [9] status=[20] [20]]
                                2018-10-23 9:09:19 PM [2] [ZONE: zone=[] number=[9] status=[SECURE]]
                                2018-10-23 9:09:19 PM [2] [---->Zone]
                                2018-10-23 9:09:18 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:09:12 PM [2] [--> Zone 9 changed status. Updating Homeseer...]
                                2018-10-23 9:09:12 PM [2] [TRIPPED]
                                2018-10-23 9:09:12 PM [2] [MapZoneStatus_V2: zoneId=[9] status=[21] zoneChanged=[False] annotation=[Z9] statusText=[TRIPPED] zoneType=[3] zoneTypeText=[AwayInt] name=[Hall Motion] area=[1] analogLoop=[254] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[2018-10-23 9:09:12 PM] isSecurityZone=[True] isArmingZone=[True] hsDeviceRef=[3254] hsParentRef=[3234] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0] highsetpoint=[0]]
                                2018-10-23 9:09:12 PM [2] [Zone [9] status=[21] [21]]
                                2018-10-23 9:09:12 PM [2] [ZONE: zone=[] number=[9] status=[NOT READY]]
                                2018-10-23 9:09:12 PM [2] [---->Zone]
                                2018-10-23 9:09:12 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:09:11 PM [2] [10/23 9:08 PM - Main Door TRIPPED nam=[]]
                                2018-10-23 9:09:11 PM [2] [EventLog=[Main Door TRIPPED]]
                                2018-10-23 9:09:11 PM [2] [Area change event raised: ]
                                2018-10-23 9:09:11 PM [2] [---->Area]
                                2018-10-23 9:09:11 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:09:11 PM [2] [--> Zone 4 changed status. Updating Homeseer...]
                                2018-10-23 9:09:10 PM [2] [TRIPPED]
                                2018-10-23 9:09:10 PM [2] [MapZoneStatus_V2: zoneId=[4] status=[21] zoneChanged=[False] annotation=[Z4] statusText=[TRIPPED] zoneType=[0] zoneTypeText=[EntryExit] name=[Main Door] area=[1] analogLoop=[254] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[2018-10-23 9:09:10 PM] isSecurityZone=[True] isArmingZone=[True] hsDeviceRef=[3248] hsParentRef=[3234] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0] highsetpoint=[0]]
                                2018-10-23 9:09:10 PM [2] [Zone [4] status=[21] [21]]
                                2018-10-23 9:09:10 PM [2] [ZONE: zone=[] number=[4] status=[NOT READY]]
                                2018-10-23 9:09:10 PM [2] [---->Zone]
                                2018-10-23 9:09:10 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:08:19 PM [2] [--> Unit 10 changed status. Updating Homeseer...]
                                2018-10-23 9:08:19 PM [2] [-->Unsolicited: Unit=[10] status=[0]/[OFF] type=[1] / []]
                                2018-10-23 9:08:19 PM [2] [-->UNIT: desc=[] number=[10] name=[chime]]
                                2018-10-23 9:08:19 PM [2] [---->Unit]
                                2018-10-23 9:08:19 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:08:18 PM [2] [--> Zone 13 changed status. Updating Homeseer...]
                                2018-10-23 9:08:18 PM [2] [SECURE]
                                2018-10-23 9:08:18 PM [2] [MapZoneStatus_V2: zoneId=[13] status=[0] zoneChanged=[False] annotation=[Z13] statusText=[SECURE] zoneType=[64] zoneTypeText=[Auxiliary] name=[Driveway Detect] area=[1] analogLoop=[149] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[2018-10-23 9:08:18 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[3258] hsParentRef=[3234] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[SECURE] hsZoneStatus=[2] lowSetpoint=[0] highsetpoint=[0]]
                                2018-10-23 9:08:18 PM [2] [Zone [13] status=[0] [0]]
                                2018-10-23 9:08:18 PM [2] [ZONE: zone=[] number=[13] status=[SECURE]]
                                2018-10-23 9:08:18 PM [2] [---->Zone]
                                2018-10-23 9:08:18 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:08:16 PM [2] [--> Output 385 changed status. Updating Homeseer...]
                                2018-10-23 9:08:16 PM [2] [-->Unsolicited: raising event for output 385]
                                2018-10-23 9:08:16 PM [2] [-->Unsolicited: updating output collection...]
                                2018-10-23 9:08:16 PM [2] [--> Unit 385 changed status. Updating Homeseer...]
                                2018-10-23 9:08:16 PM [2] [-->Unsolicited: Unit=[385] status=[0]/[OFF] type=[13] / []]
                                2018-10-23 9:08:16 PM [2] [-->UNIT: desc=[] number=[385] name=[Drive_alert]]
                                2018-10-23 9:08:16 PM [2] [---->Unit]
                                2018-10-23 9:08:16 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 9:08:16 PM [2] [--> Unit 10 changed status. Updating Homeseer...]
                                2018-10-23 9:08:16 PM [2] [-->Unsolicited: Unit=[10] status=[1]/[ON FOR 0:00:03] type=[1] / []]
                                2018-10-23 9:08:16 PM [2] [-->UNIT: desc=[] number=[10] name=[chime]]
                                2018-10-23 9:08:16 PM [2] [--> Zone 13 changed status. Updating Homeseer...]
                                2018-10-23 9:08:16 PM [2] [NOT READY]
                                2018-10-23 9:08:16 PM [2] [MapZoneStatus_V2: zoneId=[13] status=[1] zoneChanged=[False] annotation=[Z13] statusText=[NOT READY] zoneType=[64] zoneTypeText=[Auxiliary] name=[Driveway Detect] area=[1] analogLoop=[129] isNamed=[True] lastStatus=[0] lastStatusText=[] statusLastChangeDate=[2018-10-23 9:08:16 PM] isSecurityZone=[False] isArmingZone=[False] hsDeviceRef=[3258] hsParentRef=[3234] temperature=[0] humidity=[0] currentCondition=[0] currentStatusText=[NOT READY] hsZoneStatus=[0] lowSetpoint=[0] highsetpoint=[0]]
                                2018-10-23 9:08:16 PM [2] [Zone [13] status=[1] [1]]
                                2018-10-23 9:08:16 PM [2] [ZONE: zone=[] number=[13] status=[NOT READY]]
                                2018-10-23 9:08:16 PM [2] [---->Zone]
                                2018-10-23 5:41:06 PM [2] [--> Unit 38 changed status. Updating Homeseer...]
                                2018-10-23 5:41:06 PM [2] [-->Unsolicited: Unit=[38] status=[1]/[ON] type=[10] / []]
                                2018-10-23 5:41:06 PM [2] [-->UNIT: desc=[] number=[38] name=[Den heat]]
                                2018-10-23 5:41:06 PM [2] [---->Unit]
                                2018-10-23 5:41:06 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 5:41:06 PM [2] [--> Unit 33 changed status. Updating Homeseer...]
                                2018-10-23 5:41:06 PM [2] [-->Unsolicited: Unit=[33] status=[1]/[ON] type=[10] / []]
                                2018-10-23 5:41:06 PM [2] [-->UNIT: desc=[] number=[33] name=[Heat Group]]
                                2018-10-23 5:41:05 PM [2] [UNSOLICITED: ExtendedStatus]
                                2018-10-23 5:41:05 PM [2] [--> Unit 37 changed status. Updating Homeseer...]
                                2018-10-23 5:41:05 PM [2] [-->Unsolicited: Unit=[37] status=[1]/[ON] type=[10] / []]
                                2018-10-23 5:41:05 PM [2] [-->UNIT: desc=[] number=[37] name=[Dining heat]]
                                2018-10-23 5:41:05 PM [2] [---->Unit]
                                2018-10-23 9:00:21 AM [2] [Logging set to DEBUG]
                                HS3 info:
                                Help Resources 2018-10-24 10:26:01 AM Sunrise: 7:47 AM Sunset: 6:19 PM User: default
                                HOME
                                VIEW
                                TOOLS
                                PLUG-INS
                                HomeSeer Help Resources
                                HomeSeer Quick Start Guide
                                HomeSeer Help File
                                HomeSeer Support Resources
                                HomeSeer Message Board
                                Help Resources for Installed Plug-Ins and Scripts
                                Blue-Iris
                                Blue-Iris Help
                                Ultra1Wire3
                                Ultra1Wire3 Help File
                                Z-Wave
                                Help-Documentation
                                System Profile
                                MESSAGE BOARD (copy/paste section below to message board posts)
                                Current Date/Time: 2018-10-24 10:26:03 AM
                                HomeSeer Version: HS3 Pro Edition 3.0.0.435
                                Operating System: Microsoft Windows 10 Home - Work Station
                                System Uptime: 9 Days 11 Hours 23 Minutes 27 Seconds
                                IP Address: 192.168.4.4
                                Number of Devices: 133
                                Number of Events: 8
                                Available Threads: 400
                                HSTouch Enabled: True
                                Event Threads: 0
                                Event Trigger Eval Queue: 0
                                Device Exec Queue: 0
                                HSTouch Event Queue: 0
                                Email Send Queue: 0
                                Enabled Plug-Ins
                                3.1.3.33206: Blue-Iris
                                3.0.0.12: EnvCan
                                3.0.2.17: OMNI
                                3.0.6629.22233: Ultra1Wire3
                                3.0.0.36: X10
                                3.0.1.190: Z-Wave
                                HELP DESK (copy/paste section below to help desk tickets & emails)
                                Current Date/Time: 2018-10-24 10:26:05 AM
                                System Uptime: 9 Days 11 Hours 23 Minutes 28 Seconds
                                IP Address: 192.168.x.x
                                Number of Events: 8
                                Event Threads: 0
                                Email Send Queue: 0
                                License: Registered
                                License: XXXXX
                                User Name and Access Level: XXXXX (Admin)
                                WAN IP Address: x.x.x.x
                                Web Server Port: xx
                                Enabled Plug-Ins
                                3.0.0.12: EnvCan
                                3.0.2.17: OMNI
                                3.0.0.36: X10
                                3.0.1.190: Z-Wave
                                Also, I'm using an Omni output to trigger HS3 to send an email when the Omni detects a vehicle on the driveway. I set the output high for 3 seconds, and I can see in HS3 when the Omni output last triggered, but HS3 doesn't always send an email. Am I doing something wrong?
                                Since my only Homeseer installation is at my vacation home, I don't get enough time to extend it's usefulness; there are always many Mr.Fixit things that compete for my attention.
                                Thanks to all for your valuable contributions; Pete, you've been a goldmine of information for me!