    Arming Status not right

    I set up a HS device for an Area and put in the arming code, etc. When I use the HS device to arm/disarm it works fine. But when I used the M1 kieypad to arm/disarm, HS doesn't seem to know about it. This is problematic as I want to run a lighting event when the system is armed.

    Thoughts?

    #2
    Ended up using outputs and M1 rules to turn them on/off depending on arming status and got it working. But still ... is this a known issue with the plugin?

    Comment


      #3
      Using the ELKRP, verify the following Elk M1 "Globals" are set to 'Yes':

      G35:=Yes (Xmit Event Log-ASCII)
      G36:=Yes (Xmit Zone Chgs-ASCII)
      G37:=Yes (Xmit Output Chgs-ASCII)
      G38:=Yes (Xmit Task Chgs-ASCII)
      G39:=Yes (Xmit Light Chgs-ASCII)
      G40:=Yes (Xmit Keypad Key Chgs)

      Regards,
      Ultrajones
      Plug-ins: UltraMon, UltraM1G, UltraCID, Ultra1Wire, UltraLog, UltraWeatherBug, UltraPioneerAVR, UltraGCIR

      Comment


        #4
        Originally posted by Ultrajones View Post
        Using the ELKRP, verify the following Elk M1 "Globals" are set to 'Yes':

        G35:=Yes (Xmit Event Log-ASCII)
        G36:=Yes (Xmit Zone Chgs-ASCII)
        G37:=Yes (Xmit Output Chgs-ASCII)
        G38:=Yes (Xmit Task Chgs-ASCII)
        G39:=Yes (Xmit Light Chgs-ASCII)
        G40:=Yes (Xmit Keypad Key Chgs)

        Regards,
        Ultrajones
        I bet this was it. G40 was not enabled.