    here is the issue regarding the fault/clearing of zones: the number of digits which represent a zone number isn't matching my current logic.

    from the following msg, the second section "106" (which i use as the zone number) doesn't match zone 6 which you created in the plugin. it also doesn't match the 06 in the alpha message.

    Apr-11 7:09:33 AM Vista Alarm [00010001000000000A--],106,[f707000400068000080200000d0000],"FAULT 06 FAMILY MOTION DETECTOR "
    how many zones do you have programmed into the panel?

    how many zones in partition 1 and partition 2?

    when you bypass zone 6 from a physical keypad, what do you enter? i'm curious if you enter 06 or 006 for the zone number
    Last edited by mnsandler; April 11, 2016, 03:42 PM.
    Mark

    HS3 Pro 4.2.19.5
    Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
    Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
    Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

    Comment


      #17
      1) In order to verify the number of partitions, I used my "main" keypad and used the "GOTO" command ( code + * + partition # (1-8). I tried all partition numbers and got the following:
      code * 0 => "LOG-ON TO P1 PART.1 COMPLETE"
      code * 1 => "LOG-ON TO P1 PART.1 COMPLETE"
      code * 2 => "LOG-ON TO MASTER PART.9 COMPLETE"
      all others, 3-8 I got nothing on Alpha display.

      So I guess I have 2 partitions.
      Does the fact that I have a STAY button which only arms the perimeter mean that that is a partition????
      ----
      2)
      Some additional info:

      I pressed 1 and 3 for 5 seconds on each of our keypads to get their 2 digit address.

      The first floor keypad said 00
      The second floor keypad said 31
      The ad2serial is set for 18

      -----
      From the first floor keypad using #93 mode, I determined the following configuration:

      Device 1 Alpha Console
      Device 2 Alpha Console
      Device 3 RF Expander
      Device 4 is Voice Module
      Device 18 is Alpha Console

      ZONES: all seemed to be associated with Partition 1

      POINT 01 SMOKE DETECTORS
      POINT 02 FRONT DOOR
      POINT 03 GARAGE ENTRY DOOR
      POINT 04 KITCHEN SLIDING DOOR
      POINT 05 GARAGE MOTION DETECTOR
      POINT 06 FAMILY ROOM MOTION DETECTOR
      POINT 07 LIVING ROOM MOTION DETECTOR
      POINT 08 BASEMENT MOTION DETECTOR
      POINT 09 FAMILY ROOM WINDOWS
      POINT 10 LIVING ROOM WINDOWS
      POINT 11 DINING ROOM WINDOWS
      POINT 12 ZONE 12

      3) I bypass zone 6 with 06 not 006

      Comment


        #18
        thanks for the info. I don't understand what Partition 2 is used for but its not important right now.

        Sean and I are are trying to resolve the ad2usb messages you posted vs what a 128p panel produces. The 128p uses a 3 digit zone number. the 50p uses a 2 digit code but yours seems to acting different than other 50p panels i have run into.

        stay tuned
        Mark

        HS3 Pro 4.2.19.5
        Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
        Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
        Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

        Comment


          #19
          Mark,
          I decided to power cycle the panel. Here are the messages. I didn't see any 106 interestingly. I hope this helps.

          Apr-11 10:13:29 PM Vista Alarm !Sending.done Apr-11 10:13:28 PM Vista Alarm !Sending.done Apr-11 10:13:28 PM Vista Alarm Sending [code]+11 Apr-11 10:13:28 PM Device Control Device: Vista Alarm System Status to Disarm (101) by/from: CAPI Control Handler Apr-11 10:13:13 PM Vista Alarm 0529656,80 Apr-11 10:12:48 PM Vista Alarm 0850944,0f Apr-11 10:12:45 PM Vista Alarm 0138492,80 Apr-11 10:12:04 PM Vista Alarm 0029525,08 Apr-11 10:12:01 PM Vista Alarm 0029576,d9 Apr-11 10:11:25 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:25 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:25 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:24 PM Vista Alarm 0537348,82 Apr-11 10:11:23 PM Vista Alarm Setting System to Faulted Apr-11 10:11:23 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:11:22 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:22 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:22 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:21 PM Vista Alarm Setting System to Faulted Apr-11 10:11:21 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:11:20 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:20 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:20 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:18 PM Vista Alarm Setting System to Faulted Apr-11 10:11:18 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:11:15 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:15 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:15 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:14 PM Vista Alarm Setting System to Faulted Apr-11 10:11:14 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:11:11 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:11 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:11 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:09 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:11:09 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:11:09 PM Vista Alarm Setting System to Faulted Apr-11 10:11:09 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:11:09 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:11:09 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:11:09 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:11:07 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:11:07 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:11:07 PM Vista Alarm Setting System to Faulted Apr-11 10:11:07 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:44 PM Vista Alarm 0577590,00 Apr-11 10:10:41 PM Vista Alarm 0577590,80 Apr-11 10:10:38 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:38 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:38 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:34 PM Vista Alarm 0627917,00 Apr-11 10:10:34 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:34 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:34 PM Vista Alarm Setting System to Faulted Apr-11 10:10:34 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:32 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:32 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:32 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:31 PM Vista Alarm 0314752,42 Apr-11 10:10:30 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:30 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:30 PM Vista Alarm Setting System to Faulted Apr-11 10:10:30 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:22 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:22 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:22 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:20 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:20 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:20 PM Vista Alarm Setting System to Faulted Apr-11 10:10:20 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:20 PM Vista Alarm 0131072,30 Apr-11 10:10:20 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:20 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:20 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:18 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:18 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:18 PM Vista Alarm Setting System to Faulted Apr-11 10:10:18 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:17 PM Vista Alarm 0063392,93 Apr-11 10:10:16 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:16 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:16 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:14 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:14 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:14 PM Vista Alarm Setting System to Faulted Apr-11 10:10:14 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:13 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:13 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:13 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:10:11 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:10:11 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:10:11 PM Vista Alarm Setting System to Faulted Apr-11 10:10:11 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:10:00 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:10:00 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:10:00 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:09:58 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:09:58 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:09:58 PM Vista Alarm Setting System to Faulted Apr-11 10:09:58 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:09:57 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:09:57 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:09:57 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:09:55 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:09:55 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:09:55 PM Vista Alarm Setting System to Faulted Apr-11 10:09:55 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:09:53 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:09:53 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:09:53 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:09:51 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:09:51 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:09:51 PM Vista Alarm Setting System to Faulted Apr-11 10:09:51 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:09:48 PM Vista Alarm 0537348,85 Apr-11 10:09:48 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:09:48 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:09:48 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:09:46 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:09:46 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:09:46 PM Vista Alarm Setting System to Faulted Apr-11 10:09:46 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:08:47 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:08:47 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:08:47 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:08:45 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:08:45 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:08:45 PM Vista Alarm Setting System to Faulted Apr-11 10:08:45 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:08:33 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:08:33 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:08:33 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:08:33 PM Vista Alarm 0278823,00 Apr-11 10:08:30 PM Vista Alarm [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR " Apr-11 10:08:30 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:08:30 PM Vista Alarm Setting System to Faulted Apr-11 10:08:30 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:08:23 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:08:23 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:08:23 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:08:19 PM Vista Alarm [00010001000000000A--],003,[f70700040003800008020000000000],"FAULT 03 GARAGE ENTRY DOOR " Apr-11 10:08:19 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:08:19 PM Vista Alarm Setting System to Faulted Apr-11 10:08:19 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:08:12 PM Vista Alarm 0550963,04 Apr-11 10:08:06 PM Vista Alarm 0605429,84 Apr-11 10:07:53 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:07:53 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:07:53 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:07:47 PM Vista Alarm [00010001000000000A--],003,[f70700040003800008020000000000],"FAULT 03 GARAGE ENTRY DOOR " Apr-11 10:07:47 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:07:47 PM Vista Alarm Setting System to Faulted Apr-11 10:07:47 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:07:43 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:07:43 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:07:43 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:07:36 PM Vista Alarm 0552735,84 Apr-11 10:07:36 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm [00010001000000003A--],003,[f70700040003800c08020000000000],"****DISARMED**** ZONES FAULTED " Apr-11 10:07:35 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:07:35 PM Vista Alarm [00010001000000000A--],003,[f70700040003800008020000000000],"FAULT 03 GARAGE ENTRY DOOR " Apr-11 10:07:35 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:07:35 PM Vista Alarm Zone changed. Set device Vista Zone 3 to Value=Fault Apr-11 10:07:35 PM Vista Alarm Setting System to Faulted Apr-11 10:07:35 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm [10010101000000000A--],0c0,[f700000400c0011008020000000000],"Log-on to P1 Part. 1 Complete" Apr-11 10:07:35 PM Vista Alarm Ignoring Message Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm !Sending.done Apr-11 10:07:35 PM Vista Alarm Setting System to Disarmed-Ready Apr-11 10:07:35 PM Vista Alarm Clearing all zones for Ready mode. Apr-11 10:07:35 PM Vista Alarm Setting Partition 2 to Disarmed-Ready Apr-11 10:07:35 PM Vista Alarm [00010101000000000A--],0c0,[f700000400c0010008020000000000],"Log-on to MASTERPart. 9 Complete" Apr-11 10:07:35 PM Vista Alarm Ignoring Message Apr-11 10:07:35 PM Vista Alarm Sending [code]+*0 Apr-11 10:07:33 PM Vista Alarm Sending * Apr-11 10:07:30 PM Vista Alarm Sending [code]+*2 Apr-11 10:07:30 PM Vista Alarm !Sending.done Apr-11 10:07:30 PM Vista Alarm !Sending.done Apr-11 10:07:30 PM Vista Alarm [00010001000000003A--],000,[f70700040000800c08020000000000],"****DISARMED****Hit * for faults" Apr-11 10:07:30 PM Vista Alarm Processing msg on Partition 2 Apr-11 10:07:30 PM Vista Alarm Sending [code]+*0 Apr-11 10:07:28 PM Vista Alarm Sending * Apr-11 10:07:26 PM Vista Alarm Sending [code]+*2 Apr-11 10:07:26 PM Vista Alarm Setting System to Faulted Apr-11 10:07:26 PM Vista Alarm Setting Partition 2 to Faulted Apr-11 10:07:12 PM Vista Alarm 0942468,bd Apr-11 10:06:57 PM Vista Alarm 0131319,00 Apr-11 10:06:54 PM Vista Alarm 0131319,a0 Apr-11 10:06:36 PM Vista Alarm 0550963,04 Apr-11 10:06:28 PM Vista Alarm 0577590,00 Apr-11 10:06:26 PM Vista Alarm 0577590,80 Apr-11 10:06:23 PM Vista Alarm !Ready. Press ! for configuration. Apr-11 10:06:23 PM Vista Alarm !UART init. Apr-11 10:06:23 PM Vista Alarm !Reading configuration. Apr-11 10:06:23 PM Vista Alarm !www.AlarmDecoder.com Apr-11 10:06:23 PM Vista Alarm !For support email AlarmDecoder@support.nutech.com Apr-11 10:06:23 PM Vista Alarm !By Sean Mathews Apr-11 10:06:22 PM Vista Alarm !Reproduction without permission is prohibited Apr-11 10:06:22 PM Vista Alarm !Copyright (C) 2008-2015 Nu Tech Software Solutions, Inc. Apr-11 10:06:22 PM Vista Alarm !Ademco Keypad Emulator V2.2a.8.2 Apr-11 10:06:22 PM Vista Alarm !boot....................?! Apr-11 10:06:18 PM Vista Alarm !sn:00000663 Apr-11 10:06:07 PM Vista Alarm [10010401000100003A--],006,[f70700040006845c08020000000000],"SYSTEM LOBAT "

          Comment


            #20
            The above log isnt displayed correctly. The line braks are missing. Can you clean it up or repost
            Mark

            HS3 Pro 4.2.19.5
            Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
            Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
            Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

            Comment


              #21
              Mark,
              I attached new log as file. This was from today.
              Attached Files

              Comment


                #22
                well that looks better regarding the zone numbers, are the zone devices tracking properly now?

                are the arm/disarm statuses tracking for Partition 1? all i see is Part. 2 activity
                Mark

                HS3 Pro 4.2.19.5
                Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                Comment


                  #23
                  Mark,
                  The zones are still not tracking. Did the information I gave you in a few posts ago regarding the GOTO partition give you a better idea of my configuration.
                  I wish the installer would have competed those grids at the end of the docs he left detailing how this system was configured.

                  I am still seeing partition 2 in the log but when I went through the programming for the zones, it said that they were associated with P1 so I am very confused. It seems from the line below ( from a few posts back )
                  code * 2 => "LOG-ON TO MASTER PART.9 COMPLETE"
                  that I have a partition 9, not 2? What can I do to get a definitive handle on this configuration so we can get the zone update working?

                  Comment


                    #24
                    the addresses you assigned to the partitions in the plugin don't make sense. my guess is you don't actually have a keypad assigned to address 1 or 2. correct me if this is wrong.

                    lets do the following in the plugin config:
                    set the address of Partition 2 to Disabled - we don't need this for zone control
                    set the address of Partition 1 to 31.
                    retest zone faulting.
                    if that doesn't help set Part 1 address in plugin to 0
                    retest

                    within the panel programming
                    make sure address 18 is assigned to partition 1
                    create a new user code (within the panel) that only has access to Partition 1 (ie not a master code or system admin code)
                    enter this user code into the partition 1 user code field

                    retest
                    Mark

                    HS3 Pro 4.2.19.5
                    Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                    Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                    Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                    Comment


                      #25
                      Mark,
                      I disabled partition and once done, all of the zone statuses changed to normal. I am remotely connected to my pc so I cannot fault a zone and then disarm to see if the zone returns to normal status . I will do that when I get home. I will see what happens before proceeding with your instructions.

                      With regard to the keypad addresses:

                      From the first floor keypad using #93 mode, I determined the following configuration:

                      Device 1 Alpha Console
                      Device 2 Alpha Console
                      Device 3 RF Expander
                      Device 4 is Voice Module
                      Device 18 is Alpha Console

                      I pressed 1 and 3 for 5 seconds on each of our keypads to get their 2 digit address.

                      The first floor keypad said 00
                      The second floor keypad said 31
                      The ad2serial is set for 18

                      So maybe you are correct with the keypad idea. From the information above, is my keypad at 1 or 0? One way says device 1 is keypad, the other says its address 00????

                      Comment


                        #26
                        ok. we're making progress.

                        regarding device # vs address: the plugin only cares about "addresses". Addresses are coded into the ad2usb msgs and thus the addresses are what is needed to decode them.

                        My guess is if you change the plugin partition 1 to address 0 or 31 (assuming both are associated with partition 1 in the panel programming), the zone tracking will work.

                        one thing you can try remotely is doing a Bypass on a zone. if the plugin updates the status correctly then we are really making progress. you can Disarm to return the zone to Normal.
                        Mark

                        HS3 Pro 4.2.19.5
                        Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                        Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                        Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                        Comment


                          #27
                          Mark,
                          Disabling Partition 2 on the Plugin config page only:
                          1) Zones are tracking
                          2) Messages in the log file now refer only to partition 1, not partition 2 as before
                          3) I can bypass a zone, status goes to bypassed, arm system as STAY, and upon disarm and say closing faulted door, the zone status goes back to normal
                          4) Partition 1 device address is still set to 1 but earlier you said
                          "set the address of Partition 1 to 31." ..."to 0". Do you still want me to try that? Any other tests I need to do to confirm proper integration? Things seem to be working but I want it to be configured properly so that if anything say changes in the plugin that currently tolerates my "goofy" config it won't stop working in the future.

                          5) BTW, I'm still "weirded-out" by that Partition 9 stuff in my previous posts.
                          Last edited by cyber_jocky; April 13, 2016, 07:18 PM. Reason: add one more question

                          Comment


                            #28
                            1. good
                            2. good
                            3. good
                            4. please try address 0 for Partition 1, then address 31 and see if 1,2,3 still work
                            5. these extra partitions are apparently normal when a professional installer does the config. they can be used to notify a monitor company of certain events, or other alerts that are independent of the primary partition (#1). I would just ignore it unless the installer gave you specific instructions. the plugin will just ignore these msgs.

                            i don't think there is anything else to test except the other arm buttons.

                            i think we are almost there
                            Mark

                            HS3 Pro 4.2.19.5
                            Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                            Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                            Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                            Comment


                              #29
                              Mark,
                              Changed partition 1 to address 0 and everything worked ( same as address 1 ).
                              [00010001000000000A--],006,[f70700040006800008020000000000],"FAULT 06 FAMILY MOTION DETECTOR "


                              Processing msg on Partition 1

                              Setting it to 31 did not work. No zone tracking.

                              [10010001000000003A--],006,[f70700040006801c08020000000000],"****DISARMED**** READY TO ARM "


                              Ignoring Message
                              So, should I keep partition 1 address as 0 or 1?

                              Also, I am seeing an interesting phenomenon on my 2nd floor alpha keypad. This is the one that I think is addressed as 31. Both the armed ( red) and ready ( green ) led's are on. I wonder if setting HS config to address 31 caused this. Not sure what to do here. One thing that makes it more difficult is that the installer ( years ago ) convinced me to let him set the screen on this keypad up so that it is blank ( he said you could see it from the front door and wanted to hide the alarm state ) . Well that sounded good, but now, the keys seem to work and their lights work too but nothing shows up on the lcd. I thought that the lcd used to light up once a key was hit but not now. Could this blank screen business be an indicator of a system configuration issue? I'm not sure how to figure out if it is related to the 31 address I setup or what. Any ideas on that?

                              Comment


                                #30
                                lets stick with Address 0 for partition 1 in the plugin. address 1 must be used for one of your other alarm devices.

                                if you find a keypad manual you should be able to restore the lcd screen. not sure about the red/green issue. it might be worth resetting the keypad (again you need the manual for your keypad model)

                                i believe addr 31 is some kind of universal address to show all msgs from all devices. i wouldn't change anything related to that.