    Stat not showing current temp

    Everything works, but the Stat does not show the current temp.
    Any suggestions?

    #2
    It sounds like perhaps the reporting links did not get fully written to the thermostat for communication between. You can use the control panel "read links" and "write links" functions to attempt to fix this.

    Other items to consider are making sure you have a dual band device close enough to the thermostat that those temp change broadcasts are making it successfully to the hub (or plm) you're using.

    Finally the thermostat hardware itself controls when it sends a temp update and most seem to require a 2 degree change before that happens. Some people have worked around this by polling the thermostat every so often to pull in the current values.
    HS 3.0.0.435 (PRO)
    Hardware: Napco GEM-P9600 | VenstarT1800 w/Insteon 2441V adapter | Insteon PLM
    Plugins HS3: Napco Gemini (mine) | Insteon Thermostat (mine) | Insteon Plug-in (mnsandler) | HSTouch Server (HST)
    Platform: Windows 10 Pro 64bit, core2 duo 2.0Ghz, 4GB memory
    http://www.kazteel.com/

    Comment


      #3
      Thanks for the reply.
      I used Easy Trigger to set polling for the stat... works perfectly.