APC Back-UPS XS 1500 Not Working

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    APC Back-UPS XS 1500 Not Working

    I just installed the plugin and it does not appear to to see my UPS.

    It is connected via USB to my Windows 10 Pro system and I have the APC PowerChute Personal Addition up and running.

    Do I need to NOT run the APC application? I'll try shutting it down.

    #2
    I used the Task Manager and killed all of the PowerChute processes and it still does not see my UPS. I also tried to restart HS3 with no luck?

    Startup log reports:

    Code:
    3/4/2018 6:08:43 PM ~!~Info~!~Plugin BLUPS has connected. IP:127.0.0.1:63145
    3/4/2018 6:08:43 PM ~!~BLUPS start~!~Initializing BLUPS...
    3/4/2018 6:08:44 PM ~!~BLUPS start~!~BLUPS version is: 2.0.22.0
    3/4/2018 6:08:44 PM ~!~BLUPS start~!~Loaded configuration successfully
    3/4/2018 6:08:44 PM ~!~BLUPS start~!~UPS battery has been detected on the system
    3/4/2018 6:08:44 PM ~!~BLUPS start~!~Checking devices owned by BLUPS
    3/4/2018 6:08:44 PM ~!~BLUPS start~!~BLUPS plug-in has been initialized
    3/4/2018 6:08:44 PM ~!~Plug-In~!~Finished initializing plug-in BLUPS
    I note that there are PORT numbers. I guess at this point I should try and find if there is any documentation. Do I need to do anything with my firewall with these port numbers? IP:127.0.0.1:63145

    The log says it sees my UPTS:

    3/4/2018 6:08:44 PM ~!~BLUPS start~!~UPS battery has been detected on the system

    Comment


      #3
      I completely uninstalled PowerChute and rebooted system and it still is not reporting the UPS data?

      Comment


        #4
        Try this

        1. Disable plugin
        2. Edit hspi_BLUPS.ini and change debugLevel=true
        3. Save INI file
        4. Re-enable plugin

        Let the plugin run a few minutes, then disable debug logging

        Attach the BLUPS-Detailed.log zipped
        It is in the HS3 root folder
        Cheers,
        Bob
        Web site | Help Desk | Feature Requests | Message Board

        Comment


          #5

          Comment


            #6
            Originally posted by Blade View Post
            Try this

            1. Disable plugin
            2. Edit hspi_BLUPS.ini and change debugLevel=true
            3. Save INI file
            4. Re-enable plugin

            Let the plugin run a few minutes, then disable debug logging

            Attach the BLUPS-Detailed.log zipped
            It is in the HS3 root folder

            Ok here it is attached. [ Attachment moved to Case on Blades Support Site ]
            Last edited by rjbur; March 6, 2018, 02:50 PM.

            Comment


              #7
              OK do me a favor
              Log a ticket on my help desk and attach the zipped log to the ticket
              That way I have a record of the issue
              Cheers,
              Bob
              Web site | Help Desk | Feature Requests | Message Board

              Comment


                #8
                Originally posted by Blade View Post
                OK do me a favor
                Log a ticket on my help desk and attach the zipped log to the ticket
                That way I have a record of the issue
                As you have requested, so it has been done Lord Vader. May you bring the force of the power to banish this troublesome issue from our site...

                Ok so I couldn't resist with your Avatar.

                I look fore t' yer assistance, render no quarter, grant no parley matey. Oh, 'n where be th' rum?

                Comment


                  #9
                  I found the problem!!!

                  It seems that BLUPS does not like the APC UPS driver.

                  I opened the Device Manager and

                  1) Clicked on 'Batteries' to expand list

                  2) Right-Clicked on 'APC UPS'

                  3) Selected 'Update Driver'

                  4) Selected 'Browse m y computer for driver...'

                  5) Selected 'Let me pick from a list...'

                  The following list appears:

                  APC UPS
                  HID UPS Battery
                  HID-compliant device

                  6) Select 'HID UPS Batter'

                  7) Next and Close

                  The Status page now shows:

                  Power Status On AC Power
                  Battery Level High
                  Battery Percentage 100%
                  Life Remaining 54 minutes
                  Last Power Failure Not Set
                  Last Power Restore 3/13/2018 5:43:14 PM

                  Comment


                    #10
                    Thanks for documenting rjbur. This was my issue as well and your steps seem to have fixed it.