    2420M Motion sensor questions

    After spending half a day trying to figure out this device, I've concluded the following: ANY communication from HS to the 2420M is successful ONLY if the 2420M is in link mode.

    So, even for manually adding the 2420M (Tap-add doesn't work), the 2420M needs to be in linking mode. To program the various features of the 2420M (custom settings), it has to be in linking mode. To reread the device's links, it has to be in linking mode.

    If this is right, it's a pain: early on, you'll want to experiment with different settings and you'll have to put the device back into linking mode every time. Strange design...

    Can anyone validate my finding?

    #2
    Insteon plugin, 2420M custom settings

    Is the Sensitivity custom setting related to Night/Day or Detection Range?

    Has anyone noticed a real change in brightness after changing the LED Brightness custom setting?

    Comment


      #3
      2420M Motion sensor default values

      In the 2420M Custom Settings,it says " (* indicates default setting) ", but I can't see "*" in the pull down lists. What's up?

      Comment


        #4
        Originally posted by claude View Post
        In the 2420M Custom Settings,it says " (* indicates default setting) ", but I can't see "*" in the pull down lists. What's up?

        I'll have to add the asterisk (*)

        Originally posted by claude View Post
        After spending half a day trying to figure out this device, I've concluded the following: ANY communication from HS to the 2420M is successful ONLY if the 2420M is in link mode.

        So, even for manually adding the 2420M (Tap-add doesn't work), the 2420M needs to be in linking mode. To program the various features of the 2420M (custom settings), it has to be in linking mode. To reread the device's links, it has to be in linking mode.

        If this is right, it's a pain: early on, you'll want to experiment with different settings and you'll have to put the device back into linking mode every time. Strange design...

        Can anyone validate my finding?
        correct, linking mode is required. and i can't trigger this from the sw, i tried. The device is transmit only in normal operation. link mode is required in order to program or read the device.

        Originally posted by claude View Post
        Is the Sensitivity custom setting related to Night/Day or Detection Range?

        Has anyone noticed a real change in brightness after changing the LED Brightness custom setting?
        from the tech manual regarding Sensitivity
        The unit only uses the intensity value when in night-only mode (JP-4) to determine if it is "night". The higher the value, the darker it needs to be for the unit to see night. Default value is 0x23
        the led brightness does change but only with large changes to the setting. default is 64
        Mark

        HS3 Pro 4.2.19.5
        Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
        Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
        Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

        Comment


          #5
          Originally posted by mnsandler View Post
          The unit only uses the intensity value when in night-only mode (JP-4) to determine if it is "night". The higher the value, the darker it needs to be for the unit to see night. Default value is 0x23
          Using the plugin, I have Night Only = Off and I am still getting On/Off commands for (artificially created) day/night transitions.

          You mentionned "... tech manual regarding Sensitivity ...". I have a support call outstanding at Skylink; I'm hoping to get more detailed info. What documentation are you referring to?

          Comment


            #6
            Originally posted by claude View Post
            Using the plugin, I have Night Only = Off and I am still getting On/Off commands for (artificially created) day/night transitions.

            You mentionned "... tech manual regarding Sensitivity ...". I have a support call outstanding at Skylink; I'm hoping to get more detailed info. What documentation are you referring to?
            I have access to to insteon developer documentation, unfortunately i can't share it.

            what is the firmware ver of the motion sensor? 82 or greater is the newer one which i am still working on regarding setting the day/night mode via the plugin

            have you changed the day/night jumper?
            Mark

            HS3 Pro 4.2.19.5
            Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
            Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
            Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

            Comment


              #7
              F/W versiopn: 32 (did you really mean 82?). I've only closed JP5.

              Comment


                #8
                you have a v1 motion sensor, v2 starts at firmware 82.

                have you seen the following manual from the smarthome site

                http://www.smarthome.com/manuals/2420mqs.pdf

                jp5 doesn't do anything. check jp3 for night only mode
                Mark

                HS3 Pro 4.2.19.5
                Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                Comment


                  #9
                  I'm totally confused. My unit has the following sticker on the back: "1610 REV 2.0". I double checked with Smarthome and they say it's a version 2.

                  I had heard that V2 added the Off count down, which my unit has.

                  The link to the manual you sent me describes a V1 I believe.

                  If you follow this link http://www.smarthome.com/2420M/Wirel...-Sensor/p.aspx and go down to "Manuals/Software" then click on the link Prior revision documents, then select "Rev 1.0 Quick Start Guide", you'll find the manual you referred to in your message, but it's 1.0.

                  My unit's circuit board looks exactly like the one displayed in the current version.

                  All this doesn't explain why my unit says F/W 32, unless they reset the number with Rev 2.0.

                  What does the sticker on the back of your unit say?

                  Comment


                    #10
                    my V2 sticker says 3809 rev 3.04 hs reports firmware 82

                    m V1 sticker says 1909 Rev 1.2 hs reports firmware 24

                    my V2 did have a BETA sticker so maybe they did reset the firmware. who knows. I'll send an email to my smarthome contact to verify

                    please post a screen shot of your motion sensor setup page
                    Mark

                    HS3 Pro 4.2.19.5
                    Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                    Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                    Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                    Comment


                      #11
                      please try the night only=on setting? maybe i got the values backwards
                      Mark

                      HS3 Pro 4.2.19.5
                      Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                      Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                      Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                      Comment


                        #12
                        2420M setup attached
                        Attached Files

                        Comment


                          #13
                          Originally posted by claude View Post
                          2420M setup attached
                          are the LED and On Only options changing as expected?
                          Mark

                          HS3 Pro 4.2.19.5
                          Hardware: Insteon Serial PLM | AD2USB for Vista Alarm | HAI Omnistat2 | 1-Wire HA7E | RFXrec433 | Dahua Cameras | LiftMaster Internet Gateway | Tuya Smart Plugs
                          Plugins: Insteon (mine) | Vista Alarm (mine) | Omnistat 3 | Ultra1Wire3 | RFXCOM | HS MyQ | BLRadar | BLDenon | Tuya | Jon00 Charting | Jon00 Links
                          Platform: Windows Server 2022 Standard, i5-12600K/3.7GHz/10 core, 16GB RAM, 500GB SSD

                          Comment


                            #14
                            Originally posted by mnsandler View Post
                            are the LED and On Only options changing as expected?
                            All are behaving as expected. Only odd thing is that I've set "On only" and it seems I'm getting an Off from the 2420M (only) when I put it in link mode.

                            Comment


                              #15
                              Suggestion for debugging

                              I've been looking back at my logs to validate things. I set and unset 2420M custom settings. I realize now looking back at my logs, even in detailed debug, that there is no entry defining what was actually changed. The only entry is
                              Sending command 02 62 13 EF 65 10 2E 00 00 03 01 00 00 00 00 00 00 00 00 00 00 00 to PLM
                              It's not easy to figure out what changes were sent out to the 2420M, not having the programming documentation, unless one writes down everything.

                              Would it be feasible to include some litterals in the log describing what changes are being requested, as you do with incoming messages when you describe what the command is, whether its a direct or broadcast, etc.

                              Comment