Hi All,
First time posting on the forum, I have a couple of Keypadlinc Controllers that appear to not properly register using the plugin. Most of my Keypadlincs allow both control and status updates from each button, however the two that I am having issues with don't update button status. After hard resetting and repairing these keypads to homeseer, the only button that I am able to see the status updates for is the A/Main button. Looking at the link list for each device shows that they are missing the "Button X has local control reporting to HomeSeer" lines. Is there a trick to get these keypads to have these lines added back in so i can have Homeseer respond to these button presses? Thanks.
Working Keypad (Office Keypad)
Link #21 Button A/Load controls Bathroom Keypad (40.C8.FF)
Link #29 Button H controls Hallway Overhead Light Unknown Group/Button Name #8 (41.AE.0D)
Link #2 Button H controls Hallway Keypad (40.FD.88)
Link #25 Button H controls Pete's Bedroom Keypad Button H (40.F9.F5)
Link #23 Button H controls Joshua's Bedroom Keypad Button H (40.FB.5B)
Link #27 Button H controls Bathroom Keypad Button H (40.C8.FF)
Link #3 Button A/Load has local control reporting to HomeSeer
Link #4 Button B has local control reporting to HomeSeer
Link #5 Button C has local control reporting to HomeSeer
Link #6 Button D has local control reporting to HomeSeer
Link #7 Button E has local control reporting to HomeSeer
Link #8 Button F has local control reporting to HomeSeer
Link #9 Button G has local control reporting to HomeSeer
Link #10 Button H has local control reporting to HomeSeer
Link #22 Button A/Load is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level: 0%, Ramp Rate: .5 Sec.
Link #20 Button A/Load is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level: 0%, Ramp Rate: .5 Sec.
Link #11 Button A/Load is controlled by HomeSeer using RF PLM Group #254 (HomeSeer All Devices Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #12 Button A/Load is controlled by HomeSeer using RF PLM Group #9 (Button Control Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #13 Button B is controlled by HomeSeer using RF PLM Group #10 (Button Control Group) - On Level : On
Link #14 Button C is controlled by HomeSeer using RF PLM Group #11 (Button Control Group) - On Level : On
Link #15 Button D is controlled by HomeSeer using RF PLM Group #12 (Button Control Group) - On Level : On
Link #16 Button E is controlled by HomeSeer using RF PLM Group #13 (Button Control Group) - On Level : On
Link #17 Button F is controlled by HomeSeer using RF PLM Group #14 (Button Control Group) - On Level : On
Link #18 Button G is controlled by HomeSeer using RF PLM Group #15 (Button Control Group) - On Level : On
Link #30 Button H is controlled by Hallway Overhead Light (41.AE.0D) - On Level : On
Link #1 Button H is controlled by Hallway Keypad Button A (40.FD.88) - On Level : On
Link #26 Button H is controlled by Pete's Bedroom Keypad Button H (40.F9.F5) - On Level : On
Link #24 Button H is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level : On
Link #28 Button H is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level : On
Link #19 Button H is controlled by HomeSeer using RF PLM Group #16 (Button Control Group) - On Level : On
Not Working Keypad (Hallway Keypad)
Link #12 Button A controls Hallway Overhead Light (41.AE.0D)
Link #20 Button A controls Pete's Bedroom Keypad Button H (40.F9.F5)
Link #18 Button A controls Office Keypad Button H (40.FC.C6)
Link #16 Button A controls Joshua's Bedroom Keypad Button H (40.FB.5B)
Link #14 Button A controls Bathroom Keypad Button H (40.C8.FF)
Link #10 Button B controls Living Room Lights (3E.84.35)
Link #7 Button B controls Kitchen Keypad Button B (40.C9.93)
Link #9 Button B controls Living Room Keypad Button B (40.FA.E6)
Link #5 Load has local control reporting to HomeSeer
Link #13 Button A is controlled by Hallway Overhead Light (41.AE.0D) - On Level: 100%, Ramp Rate: 6 Sec.
Link #21 Button A is controlled by Pete's Bedroom Keypad Button H (40.F9.F5) - On Level: 100%, Ramp Rate: .1 Sec.
Link #19 Button A is controlled by Office Keypad Button H (40.FC.C6) - On Level: 100%, Ramp Rate: .1 Sec.
Link #17 Button A is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level: 100%, Ramp Rate: .1 Sec.
Link #15 Button A is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level: 100%, Ramp Rate: .1 Sec.
Link #4 Button A is controlled by HomeSeer using RF PLM Group #0 (i2CS Registration Link) - On Level: 0%, Ramp Rate: .5 Sec.
Link #1 Button A is controlled by HomeSeer using RF PLM Group #0 (i2CS Registration Link) - On Level: 100%, Ramp Rate: .5 Sec.
Link #6 Button A is controlled by HomeSeer using RF PLM Group #254 (HomeSeer All Devices Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #3 Button A is controlled by HomeSeer using RF PLM Group #34 (Button Control Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #11 Button B is controlled by Living Room Lights (3E.84.35) - On Level : On
Link #8 Button B is controlled by Kitchen Keypad Button B (40.C9.93) - On Level : On
Link #2 Load is controlled by HomeSeer using RF PLM Group #69 (Button Control Group) - On Level : On
Josh
First time posting on the forum, I have a couple of Keypadlinc Controllers that appear to not properly register using the plugin. Most of my Keypadlincs allow both control and status updates from each button, however the two that I am having issues with don't update button status. After hard resetting and repairing these keypads to homeseer, the only button that I am able to see the status updates for is the A/Main button. Looking at the link list for each device shows that they are missing the "Button X has local control reporting to HomeSeer" lines. Is there a trick to get these keypads to have these lines added back in so i can have Homeseer respond to these button presses? Thanks.
Working Keypad (Office Keypad)
Link #21 Button A/Load controls Bathroom Keypad (40.C8.FF)
Link #29 Button H controls Hallway Overhead Light Unknown Group/Button Name #8 (41.AE.0D)
Link #2 Button H controls Hallway Keypad (40.FD.88)
Link #25 Button H controls Pete's Bedroom Keypad Button H (40.F9.F5)
Link #23 Button H controls Joshua's Bedroom Keypad Button H (40.FB.5B)
Link #27 Button H controls Bathroom Keypad Button H (40.C8.FF)
Link #3 Button A/Load has local control reporting to HomeSeer
Link #4 Button B has local control reporting to HomeSeer
Link #5 Button C has local control reporting to HomeSeer
Link #6 Button D has local control reporting to HomeSeer
Link #7 Button E has local control reporting to HomeSeer
Link #8 Button F has local control reporting to HomeSeer
Link #9 Button G has local control reporting to HomeSeer
Link #10 Button H has local control reporting to HomeSeer
Link #22 Button A/Load is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level: 0%, Ramp Rate: .5 Sec.
Link #20 Button A/Load is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level: 0%, Ramp Rate: .5 Sec.
Link #11 Button A/Load is controlled by HomeSeer using RF PLM Group #254 (HomeSeer All Devices Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #12 Button A/Load is controlled by HomeSeer using RF PLM Group #9 (Button Control Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #13 Button B is controlled by HomeSeer using RF PLM Group #10 (Button Control Group) - On Level : On
Link #14 Button C is controlled by HomeSeer using RF PLM Group #11 (Button Control Group) - On Level : On
Link #15 Button D is controlled by HomeSeer using RF PLM Group #12 (Button Control Group) - On Level : On
Link #16 Button E is controlled by HomeSeer using RF PLM Group #13 (Button Control Group) - On Level : On
Link #17 Button F is controlled by HomeSeer using RF PLM Group #14 (Button Control Group) - On Level : On
Link #18 Button G is controlled by HomeSeer using RF PLM Group #15 (Button Control Group) - On Level : On
Link #30 Button H is controlled by Hallway Overhead Light (41.AE.0D) - On Level : On
Link #1 Button H is controlled by Hallway Keypad Button A (40.FD.88) - On Level : On
Link #26 Button H is controlled by Pete's Bedroom Keypad Button H (40.F9.F5) - On Level : On
Link #24 Button H is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level : On
Link #28 Button H is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level : On
Link #19 Button H is controlled by HomeSeer using RF PLM Group #16 (Button Control Group) - On Level : On
Not Working Keypad (Hallway Keypad)
Link #12 Button A controls Hallway Overhead Light (41.AE.0D)
Link #20 Button A controls Pete's Bedroom Keypad Button H (40.F9.F5)
Link #18 Button A controls Office Keypad Button H (40.FC.C6)
Link #16 Button A controls Joshua's Bedroom Keypad Button H (40.FB.5B)
Link #14 Button A controls Bathroom Keypad Button H (40.C8.FF)
Link #10 Button B controls Living Room Lights (3E.84.35)
Link #7 Button B controls Kitchen Keypad Button B (40.C9.93)
Link #9 Button B controls Living Room Keypad Button B (40.FA.E6)
Link #5 Load has local control reporting to HomeSeer
Link #13 Button A is controlled by Hallway Overhead Light (41.AE.0D) - On Level: 100%, Ramp Rate: 6 Sec.
Link #21 Button A is controlled by Pete's Bedroom Keypad Button H (40.F9.F5) - On Level: 100%, Ramp Rate: .1 Sec.
Link #19 Button A is controlled by Office Keypad Button H (40.FC.C6) - On Level: 100%, Ramp Rate: .1 Sec.
Link #17 Button A is controlled by Joshua's Bedroom Keypad Button H (40.FB.5B) - On Level: 100%, Ramp Rate: .1 Sec.
Link #15 Button A is controlled by Bathroom Keypad Button H (40.C8.FF) - On Level: 100%, Ramp Rate: .1 Sec.
Link #4 Button A is controlled by HomeSeer using RF PLM Group #0 (i2CS Registration Link) - On Level: 0%, Ramp Rate: .5 Sec.
Link #1 Button A is controlled by HomeSeer using RF PLM Group #0 (i2CS Registration Link) - On Level: 100%, Ramp Rate: .5 Sec.
Link #6 Button A is controlled by HomeSeer using RF PLM Group #254 (HomeSeer All Devices Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #3 Button A is controlled by HomeSeer using RF PLM Group #34 (Button Control Group) - On Level: 100%, Ramp Rate: .1 Sec.
Link #11 Button B is controlled by Living Room Lights (3E.84.35) - On Level : On
Link #8 Button B is controlled by Kitchen Keypad Button B (40.C9.93) - On Level : On
Link #2 Load is controlled by HomeSeer using RF PLM Group #69 (Button Control Group) - On Level : On
Josh