    Understanding Registers Help

    I managed to get the plugin in trial installed and i believe the gateway (IP) tests fine

    Im trying to poll my Acuvim II utility meter but i have absolutely no clue how the register and values work.
    I tried random settings etc but can get any value responses
    Is anyone familiar with the AcuvimII meter?

    #2
    There is a lot more than Modbus in book, but this is what I give to new techs in the building automation industry.

    https://www.ccontrols.com/ncbpost.htm

    Comment


      #3
      1. Does your meter support Modbus?
      2. What protocol?
      3. Do you have an IP to RS485/RS232 modbus gateway or a direct serial connection to the meter?
      4. Do you have any documentation for the meter that might help us work out how to get you connected?
      Author of Highpeak Plugins | SMS-Gateway Plugin | Blue Iris Plugin | Paradox (Beta) Plugin | Modbus Plugin | Yamaha Plugin

      Comment


        #4
        Thanks guys for your response.

        I have the device connected to my ethernet network and can read the values on the web page but they update slowly and figured Modbus would be the best way to update the virtual homeseer devices..


        Here is the link to the device manual, and also a paste of the section that includes how the device comunicates its values.

        https://www.accuenergy.com/files/acu...-1040E1303.pdf



        5.2.10 Description of Modbus-TCP protocol
        The Modbus-TCP protocol is used for communication in Ethernet modules. The
        protocol sets up master/slave link in Ethernet. First, master device (client) sets
        up TCP link with slave device (server). Second, master device sends request
        frame to slave device, and slave device receives request frame and returns
        response frame to master device. Fig 5-41 displays working mode of ModbusTCP
        protocol.
        159
        Modbus Client Modbus Server
        Request Indication
        Confirmation Response
        Fig 5-41
        1. Protocol
        a. Data Frame Format
        Table 5-2
        MBAP Header Function Data
        7x8-Bits 8-Bits Nx8-Bits
        b. Modbus Application Header (MBAP Header) Field
        The Modbus application header field is the start of the data frame and consists
        of seven bytes.
        Table 5-3
        Field Length Description
        Transaction
        Identifier 2 Bytes Identification of a Modbus Request/Response transaction
        Protocol Identifier 2 Bytes Modbus protocol=0
        Length 2 Bytes Number of following bytes
        Unit Identifier 1 Byte Slave address, in the range of 0~247 decimal.
        c. Function Field
        The function code field of a message frame contains eight bits. Valid codes are
        in the range of 1~255 decimal. When a message is sent from a client to a server
        device the function code field tells the server what kind of action to perform.
        160
        Table 5-4
        Code Meaning Action
        01 Read Relay Output Status Obtain current status of Relay Output
        02 Read Digital Input(DI) Status Obtain current status of Digital Input
        03 Read Data Obtain current binary value in one or more registers
        05 Control Single Relay Output Force Relay to a state of on or off
        16 Write Multiple-registers Place specific value into a series of consecutive
        multiple-registers
        d. Data Field
        The data field is constructed using sets of two hexadecimal digits, in the range
        of 00 to FF hexadecimal. The data field of messages sent from a master to slave
        devices contains additional information which the slave must use to take the
        action defined by the function code. This can include items like discrete and
        register addresses, the quantity of items to be handled, and the count of actual
        data bytes in the field. For example, if the master requests a slave to read a
        group of holding registers (function code 03), and the data field specifies the
        starting register and how many registers are to be read. If the master writes to
        a group of registers in the slave (function code 10 hexadecimal), the data field
        specifies the starting register, how many registers to write, the count of data
        bytes to follow in the data field, and the data to be written into the registers.
        2. Format of communication
        Explanation of frame
        Table 5-5
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 06H 01H
        Fun Data start reg hi Data start reg lo Data #of regs hi Data #of regs lo
        03H 40H 00H 00H 48H
        161
        As shown in Table 5-5 the meaning of each abbreviated word is:
        Transaction identifier hi: Transaction Identifier high byte
        Transaction identifier lo: Transaction Identifier low byte
        Protocol identifier hi: Protocol Identifier high byte
        Protocol identifier lo: Protocol Identifier low byte
        Length hi: length high byte
        Length lo: length low byte
        Unit identifier: slave address
        Fun: function code
        Data start reg hi: start register address high byte
        Data start reg lo: start register address low byte
        Data #of regs hi: number of register high byte
        Data #of regs lo: number of register low byte
        a. Read Status Relay (Function Code 01)
        Function Code 01
        This function code is used to read relay status in Acuvim II series meter.
        1=On 0=Off
        There are 8 Relays in the meter, and the starting address is 0000H.
        The following query is to read 2 Relays Status of the meter Address 1.
        162
        Query
        Table 5-6 Read 2 Relays Status Query Message
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 06H 01H
        Fun Data start reg hi Data start reg lo Data #of regs hi Data #of regs lo
        01H 00H 00H 00H 02H
        Response
        The Acuvim II series meter response includes MBAP Header, function code,
        quantity of data byte and the data. For example response to read the status of
        Relay 1 and Relay 2 is shown as Table 5-6. The status of Relay 1 and Relay 2 is
        responding to the last 2 bit of the data.
        Table 5-7 Read 2 Relays Status Response Message
        Relay 1: bit0 Relay 2: bit1
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 04H 01H
        Fun Byte count Data
        01H 01H 02H
        The content of the data is,
        7 6 5 4 3 2 1 0
        0 0 0 0 0 0 1 0
        MSB LSB
        (Relay 1 = OFF , Relay 2=ON)
        163
        b. Read Status of DI (Function Code 02)
        Function Code 02
        1=On 0=Off
        There are 38 DIs in the meter, and the starting address is 0000H.
        The following query is to read the 4 DIs Status of address 1 of Acuvim II series
        meter.
        Query
        Table 5-8 Read 4 DIs Query Message
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 06H 01H
        Fun Data start
        reg hi
        Data start
        reg lo
        Data #of regs
        hi
        Data #of regs
        lo
        02H 00H 00H 00H 04H
        Response
        The response includes MBAP Header, function code, quantity of data characters
        and the data characters.
        An example response to read the status of 4 DIs (DI1=On, DI2=On, DI3=On, DI4=
        On) is shown as Table 5-9. The status of each is responding to the last 4 bit of the
        data.
        164
        Table 5-9 Read 4 DIs Response Message
        DI1: bit0 DI2: bit1 DI3: bit2 DI4: bit3
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 04H 01H
        Fun Byte count Data
        02H 01H 0FH
        The content of the data is,
        7 6 5 4 3 2 1 0
        0 0 0 0 1 1 1 1
        MSB LSB
        c. Read Data (Function Code 03)
        Query
        This function allows the users to obtain the measurement results of Acuvim II
        series meter.
        Table 5-9 is an example of reading the 6 measured data (Time) from server
        device address 1, the data start address is 1040H.
        Table 5-10 Read Time Query Message
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 06H 01H
        Fun Data start
        reg hi
        Data start
        reg lo
        Data #of
        regs hi
        Data #of
        regs lo
        03H 10H 40H 00H 06H
        165
        Response
        An example response to read Time (2006-12-18 14:15:20) is shown as Table 5-10.
        Table 5-11 Read Time Response Message
        Transaction
        identifier hi
        Transaction
        identifier lo
        Protocol
        identifier hi
        Protocol
        identifier lo Length hi Length lo Unit
        identifier
        00H 00H 00H 00H 00H 0FH 01H
        Fun Byte
        count
        Data1
        hi
        Data1
        lo
        Data2
        hi
        Data2
        lo
        Data3
        hi
        Data3
        lo
        Data4
        hi
        Data4
        lo
        Data5
        hi
        Data5
        lo
        Data6
        hi
        Data6
        lo
        03H 0CH 07H D6H 00H 0CH 00H 12H 00H 0EH 00H 0FH 00H 14H

        Comment


          #5
          Fernando, all of that was written by a programmer - Yuk.
          Most of it describes how Modbus works and isn't relevant to just using it.

          What you need is probably in Tables 6-15, 6-30, 6-31 and 6-32
          Print them and use the programming option of Windows Calculator to convert them back to Decimal Register values ie 0FFDH is Hex value 0FFD = 4093 Decimal.

          Word means it is 16 bit (one "register" only), DWord means it is 32 bit (two consecutive "registers" - but in some instances they are in reverse order).
          It doesn't say they are Signed Values (1st bit is a +/- sign) so assume not.

          16 bit Registers are a gimme because there is no possibility of Big Endian / Little Endian reverse order problems - they are either there or not. Try and find these first.

          R/W means you can read and Write from the register in this case Read means Type 3 "Read Holding Registers" and Write is Type 16 "Write Multiple Holding Registers".

          The Modbus PlugIn sorts the Type 3 / Type 16 out itself depending on whether you ask it to Read or Write but does need to be told to to write Multiple Registers (Register Write Function) because single Register Writes (Type 6) are not valid for your meter.

          Create a Modbus IP Gateway pointed at the Slave (Meter) IP address and TCP Port 502 (unless it has been changed). Set a 10 Sec poll interval for now and remember the Write Multiple Register option. Leave Big Endian and Zero Addressing blank. Note if you have multiple Modbus IP Slaves they will need a gateway setup for each.

          I would start by trying to read the Baud Rate at 1002H (4098) as it is a 16 bit register and you know what you've set it to.

          Create a device (Register) within the Gateway.
          In Status Graphics Tab you need to Add New Range Value and give it Value Limits (-65438 => 65438 should be safe although Float Values can be very large). If the value received is outside these limits the Modbus Plugin will stop with an Error. At first just try to Read the Register - set Status-Control to Status.

          In the Modbus Tab, select the Gateway you just set up, Register Type Holding Register, Slave ID 1 (usually default for IP Modbus because the IP Address itself is unique - sometimes it is still 1 even if an alternative address is able to be programmed!). Add the Register Address (4098), Return (Data) Type of Int16, leave Signed Value blank, Multiplier 1, and select Read Only and Device Enabled.

          If it doesn't work, try one register lower and then one register higher. If one of these works you can toggle Zero Based Addressing in the Gateway to offset the Registers by one and try to make them line up with the documentation.If you cant it doesn't matter - just adjust your Register List to suit. If you need to adjust this register then every other Register in the device WILL have the same Offset (unless the documentation is extremely poor).

          Note if you cant find 16 bit data at any of the three consecutive addresses it is most likely you have a comms problem of some sort as it should be easy.

          After you've found a Register and tested on a few other 16 Bit Registers move to Table 30 etc. These have an Address of two "Registers" so are either 32 Bit Float or Int32 (dword) as specified. Usually the lowest address of the two is the "Register Address" that you enter.

          Here's where it gets tricky. The two 16 Bit words are normally read and the bits lined up in order 32->17 16->1 but not always. Depending upon the vagaries of the device programmer they may be lined up in Reverse Order 16->1 32->17. The Big Endian toggle will fix this.

          Again look for something you know and keep trying until you find a a valid entry. Line Voltage is always a safe bet in an Energy Meter.

          Coils are easier - the same Register Offset will apply but data possibilities are only 0 and 1. Again the Plugin will switch to Type 1 Read or Type 5 Write Single Coils or Type 15 Write Multiple Coils as required.

          Sometimes binary data is stored in a standard Holding Register - it may even be available in both so you can choose. Sometimes you get a choice of data type ie Float in one Register Range and Int in another with both containing the same data.
          Modbus' biggest strength is that it is extremely configurable.
          Modbus' biggest weakness is that it is extremely configurable.
          You need to work out what the programmer was trying to achieve.