    Modbus devices not updating

    Hi, I installed modbus PI with a Click PLC and for a short while all seemed well, then i noticed devices not updating in HS but i am still able to control the PLC. After restarting HS3 it started to work again for a short while, i have tried deleting all devices and gateway and starting fresh but with the same problems. Any help would be much appreciated as i am new to modbus and struggling with this.


    Nick





    Current Date/Time: 30/12/2016 10:25:16
    HomeSeer Version: HS3 Pro Edition 3.0.0.298
    Operating System: Microsoft Windows 7 Professional - Work Station
    System Uptime: 0 Days 17 Hours 3 Minutes 3 Seconds
    IP Address: 192.168.0.6
    Number of Devices: 176
    Number of Events: 8
    Available Threads: 400

    Enabled Plug-Ins
    3.0.0.104: HSTouch Server
    3.8.6121.22741: Modbus
    3.0.0.21: Nest
    3.1.0.18: Sonos
    3.0.0.36: X10

    Message/Source
    Dec-30 10:34:29 Modbus Error Read error for Click Output 6
    Dec-30 10:34:29 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44357, received 44356.
    Dec-30 10:34:29 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:34:29 Modbus Error Read error for Click Compressor
    Dec-30 10:34:29 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44352, received 44351.
    Dec-30 10:34:29 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:34:29 Modbus Error Read error for Analog In 2
    Dec-30 10:34:29 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44347, received 44346.
    Dec-30 10:34:29 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44347, received 44346.
    Dec-30 10:34:29 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:34:29 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:34:29 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44342, received 44341.
    Dec-30 10:34:29 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44342, received 44341.
    Dec-30 10:34:28 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:34:28 Modbus Error Read error for Click X1
    Dec-30 10:34:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44337, received 44336.
    Dec-30 10:34:28 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:34:28 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:34:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44332, received 44331.
    Dec-30 10:34:28 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:34:28 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:34:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44327, received 44326.
    Dec-30 10:34:28 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:34:28 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:34:19 Modbus Error Read error for Click Output 6
    Dec-30 10:34:19 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44322, received 44321.
    Dec-30 10:34:19 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:34:19 Modbus Error Read error for Click Compressor
    Dec-30 10:34:19 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44317, received 44316.
    Dec-30 10:34:19 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:34:19 Modbus Error Read error for Analog In 2
    Dec-30 10:34:19 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44312, received 44311.
    Dec-30 10:34:19 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44312, received 44311.
    Dec-30 10:34:19 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:34:19 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:34:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44307, received 44306.
    Dec-30 10:34:18 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44307, received 44306.
    Dec-30 10:34:18 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:34:18 Modbus Error Read error for Click X1
    Dec-30 10:34:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44302, received 44301.
    Dec-30 10:34:18 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:34:18 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:34:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44297, received 44296.
    Dec-30 10:34:18 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:34:18 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:34:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44292, received 44291.
    Dec-30 10:34:18 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:34:18 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:34:09 Modbus Error Read error for Click Output 6
    Dec-30 10:34:09 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44287, received 44286.
    Dec-30 10:34:09 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:34:09 Modbus Error Read error for Click Compressor
    Dec-30 10:34:09 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44282, received 44281.
    Dec-30 10:34:09 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:34:09 Modbus Error Read error for Analog In 2
    Dec-30 10:34:09 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44277, received 44276.
    Dec-30 10:34:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44277, received 44276.
    Dec-30 10:34:08 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:34:08 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:34:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44272, received 44271.
    Dec-30 10:34:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44272, received 44271.
    Dec-30 10:34:08 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:34:08 Modbus Error Read error for Click X1
    Dec-30 10:34:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44267, received 44266.
    Dec-30 10:34:08 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:34:08 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:34:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44262, received 44261.
    Dec-30 10:34:08 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:34:08 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:34:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44257, received 44256.
    Dec-30 10:34:08 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:34:08 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:59 Modbus Error Read error for Click Output 6
    Dec-30 10:33:59 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44252, received 44251.
    Dec-30 10:33:59 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:59 Modbus Error Read error for Click Compressor
    Dec-30 10:33:59 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44247, received 44246.
    Dec-30 10:33:59 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:59 Modbus Error Read error for Analog In 2
    Dec-30 10:33:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44242, received 44241.
    Dec-30 10:33:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44242, received 44241.
    Dec-30 10:33:58 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:58 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44237, received 44236.
    Dec-30 10:33:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44237, received 44236.
    Dec-30 10:33:58 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:58 Modbus Error Read error for Click X1
    Dec-30 10:33:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44232, received 44231.
    Dec-30 10:33:58 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:58 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44227, received 44226.
    Dec-30 10:33:58 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:58 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44222, received 44221.
    Dec-30 10:33:58 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:58 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:49 Modbus Error Read error for Click Output 6
    Dec-30 10:33:49 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44217, received 44216.
    Dec-30 10:33:49 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:49 Modbus Error Read error for Click Compressor
    Dec-30 10:33:49 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44212, received 44211.
    Dec-30 10:33:49 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:48 Modbus Error Read error for Analog In 2
    Dec-30 10:33:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44207, received 44206.
    Dec-30 10:33:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44207, received 44206.
    Dec-30 10:33:48 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:48 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44202, received 44201.
    Dec-30 10:33:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44202, received 44201.
    Dec-30 10:33:48 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:48 Modbus Error Read error for Click X1
    Dec-30 10:33:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44197, received 44196.
    Dec-30 10:33:48 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:48 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44192, received 44191.
    Dec-30 10:33:48 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:48 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44187, received 44186.
    Dec-30 10:33:48 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:48 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:39 Modbus Error Read error for Click Output 6
    Dec-30 10:33:39 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44182, received 44181.
    Dec-30 10:33:39 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:39 Modbus Error Read error for Click Compressor
    Dec-30 10:33:39 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44177, received 44176.
    Dec-30 10:33:39 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:38 Modbus Error Read error for Analog In 2
    Dec-30 10:33:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44172, received 44171.
    Dec-30 10:33:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44172, received 44171.
    Dec-30 10:33:38 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:38 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44167, received 44166.
    Dec-30 10:33:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44167, received 44166.
    Dec-30 10:33:38 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:38 Modbus Error Read error for Click X1
    Dec-30 10:33:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44162, received 44161.
    Dec-30 10:33:38 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:38 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44157, received 44156.
    Dec-30 10:33:38 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:38 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44152, received 44151.
    Dec-30 10:33:38 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:38 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:29 Modbus Error Read error for Click Output 6
    Dec-30 10:33:29 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44147, received 44146.
    Dec-30 10:33:29 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:29 Modbus Error Read error for Click Compressor
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44142, received 44141.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:28 Modbus Error Read error for Analog In 2
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44137, received 44136.
    Dec-30 10:33:28 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44137, received 44136.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:28 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44132, received 44131.
    Dec-30 10:33:28 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44132, received 44131.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:28 Modbus Error Read error for Click X1
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44127, received 44126.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:28 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44122, received 44121.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:28 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44117, received 44116.
    Dec-30 10:33:28 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:28 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:19 Modbus Error Read error for Click Output 6
    Dec-30 10:33:19 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44112, received 44111.
    Dec-30 10:33:19 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:18 Modbus Error Read error for Click Compressor
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44107, received 44106.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:18 Modbus Error Read error for Analog In 2
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44102, received 44101.
    Dec-30 10:33:18 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44102, received 44101.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:18 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44097, received 44096.
    Dec-30 10:33:18 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44097, received 44096.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:18 Modbus Error Read error for Click X1
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44092, received 44091.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:18 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44087, received 44086.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:18 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44082, received 44081.
    Dec-30 10:33:18 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:18 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:33:09 Modbus Error Read error for Click Output 6
    Dec-30 10:33:09 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44077, received 44076.
    Dec-30 10:33:09 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:33:08 Modbus Error Read error for Click Compressor
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44072, received 44071.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:33:08 Modbus Error Read error for Analog In 2
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44067, received 44066.
    Dec-30 10:33:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44067, received 44066.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:33:08 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44062, received 44061.
    Dec-30 10:33:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44062, received 44061.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:33:08 Modbus Error Read error for Click X1
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44057, received 44056.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:33:08 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44052, received 44051.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:33:08 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:33:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44047, received 44046.
    Dec-30 10:33:08 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:33:08 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:59 Modbus Error Read error for Click Output 6
    Dec-30 10:32:59 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44042, received 44041.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:58 Modbus Error Read error for Click Compressor
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44037, received 44036.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:58 Modbus Error Read error for Analog In 2
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44032, received 44031.
    Dec-30 10:32:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44032, received 44031.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:58 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44027, received 44026.
    Dec-30 10:32:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 44027, received 44026.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:58 Modbus Error Read error for Click X1
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44022, received 44021.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:58 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44017, received 44016.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:58 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44012, received 44011.
    Dec-30 10:32:58 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:58 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:48 Modbus Error Read error for Click Output 6
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44007, received 44006.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:48 Modbus Error Read error for Click Compressor
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 44002, received 44001.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:48 Modbus Error Read error for Analog In 2
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43997, received 43996.
    Dec-30 10:32:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43997, received 43996.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:48 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43992, received 43991.
    Dec-30 10:32:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43992, received 43991.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:48 Modbus Error Read error for Click X1
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43987, received 43986.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:48 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43982, received 43981.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:48 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43977, received 43976.
    Dec-30 10:32:48 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:48 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:38 Modbus Error Read error for Click Output 6
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43972, received 43971.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:38 Modbus Error Read error for Click Compressor
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43967, received 43966.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:38 Modbus Error Read error for Analog In 2
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43962, received 43961.
    Dec-30 10:32:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43962, received 43961.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:38 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43957, received 43956.
    Dec-30 10:32:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43957, received 43956.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:38 Modbus Error Read error for Click X1
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43952, received 43951.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:38 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43947, received 43946.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:38 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43942, received 43941.
    Dec-30 10:32:38 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:38 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:28 Modbus Error Read error for Click Output 6
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43937, received 43936.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:28 Modbus Error Read error for Click Compressor
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43932, received 43931.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:28 Modbus Error Read error for Analog In 2
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43927, received 43926.
    Dec-30 10:32:28 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43927, received 43926.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:28 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43922, received 43921.
    Dec-30 10:32:28 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43922, received 43921.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:28 Modbus Error Read error for Click X1
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43917, received 43916.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:28 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43912, received 43911.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:28 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:28 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43907, received 43906.
    Dec-30 10:32:28 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:28 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:18 Modbus Error Read error for Click Output 6
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43902, received 43901.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:18 Modbus Error Read error for Click Compressor
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43897, received 43896.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:18 Modbus Error Read error for Analog In 2
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43892, received 43891.
    Dec-30 10:32:18 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43892, received 43891.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:18 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43887, received 43886.
    Dec-30 10:32:18 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43887, received 43886.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:18 Modbus Error Read error for Click X1
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43882, received 43881.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:18 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43877, received 43876.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:18 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:18 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43872, received 43871.
    Dec-30 10:32:18 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:18 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:32:08 Modbus Error Read error for Click Output 6
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43867, received 43866.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:32:08 Modbus Error Read error for Click Compressor
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43862, received 43861.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:32:08 Modbus Error Read error for Analog In 2
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43857, received 43856.
    Dec-30 10:32:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43857, received 43856.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:32:08 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43852, received 43851.
    Dec-30 10:32:08 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43852, received 43851.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:32:08 Modbus Error Read error for Click X1
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43847, received 43846.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:32:08 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43842, received 43841.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:32:08 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:32:08 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43837, received 43836.
    Dec-30 10:32:08 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:32:08 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:31:58 Modbus Error Read error for Click Output 6
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43832, received 43831.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:31:58 Modbus Error Read error for Click Compressor
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43827, received 43826.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:31:58 Modbus Error Read error for Analog In 2
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43822, received 43821.
    Dec-30 10:31:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43822, received 43821.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:31:58 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43817, received 43816.
    Dec-30 10:31:58 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43817, received 43816.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:31:58 Modbus Error Read error for Click X1
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43812, received 43811.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:31:58 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43807, received 43806.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:31:58 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:31:58 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43802, received 43801.
    Dec-30 10:31:58 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:31:58 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:31:48 Modbus Error Read error for Click Output 6
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43797, received 43796.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:31:48 Modbus Error Read error for Click Compressor
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43792, received 43791.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:31:48 Modbus Error Read error for Analog In 2
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43787, received 43786.
    Dec-30 10:31:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43787, received 43786.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:31:48 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43782, received 43781.
    Dec-30 10:31:48 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43782, received 43781.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:31:48 Modbus Error Read error for Click X1
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43777, received 43776.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:31:48 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43772, received 43771.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:31:48 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:31:48 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43767, received 43766.
    Dec-30 10:31:48 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:31:48 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:31:38 Modbus Error Read error for Click Output 6
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43762, received 43761.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:31:38 Modbus Error Read error for Click Compressor
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43757, received 43756.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:31:38 Modbus Error Read error for Analog In 2
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43752, received 43751.
    Dec-30 10:31:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43752, received 43751.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:31:38 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43747, received 43746.
    Dec-30 10:31:38 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43747, received 43746.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:31:38 Modbus Error Read error for Click X1
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43742, received 43741.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:31:38 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43737, received 43736.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16
    Dec-30 10:31:38 Modbus Error Read error for Compressor Run Time PRE
    Dec-30 10:31:38 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43732, received 43731.
    Dec-30 10:31:38 Modbus Debug Reading Slave: 2 Address: 1 HoldingRegister:Int16
    Dec-30 10:31:38 Modbus Debug Polling Modbus IP Gateway Click PLC. Reading 7 registers from slaves
    Dec-30 10:31:31 Modbus Error Read error for Click Output 6
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43727, received 43726.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 8198 Coil:Bool
    Dec-30 10:31:31 Modbus Error Read error for Click Compressor
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43722, received 43721.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 16404 Coil:Bool
    Dec-30 10:31:31 Modbus Error Read error for Analog In 2
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43717, received 43716.
    Dec-30 10:31:31 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43717, received 43716.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 28676 HoldingRegister:Float32
    Dec-30 10:31:31 Modbus Error Read error for Analog In 1 Amps
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43712, received 43711.
    Dec-30 10:31:31 Modbus Error Error in ReadFloat32: Response was not of expected transaction ID. Expected 43712, received 43711.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 28674 HoldingRegister:Float32
    Dec-30 10:31:31 Modbus Error Read error for Click X1
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43707, received 43706.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 1 DiscreteInput:Bool
    Dec-30 10:31:31 Modbus Error Read error for Compressor Run time Countdown
    Dec-30 10:31:31 Modbus Error Error in Read: Response was not of expected transaction ID. Expected 43702, received 43701.
    Dec-30 10:31:31 Modbus Debug Reading Slave: 2 Address: 51 HoldingRegister:Int16

    #2
    Devices not Updating

    I have the PI installed and have a few devices talking..... Problem is after some hours the devices stop updating. If i disable the PI and then enable it, the devices start updating again.


    Thanks


    Jay

    Comment


      #3
      This usually means your polling interval is too fast. Try to reduce the polling interval, and try to set a short (250ms) delay between each address poll in the "Advanced" settings of your gateway. Once it settles, you can start to reduce the delays to optimise your reads.
      Author of Highpeak Plugins | SMS-Gateway Plugin | Blue Iris Plugin | Paradox (Beta) Plugin | Modbus Plugin | Yamaha Plugin

      Comment


        #4
        Originally posted by beerygaz View Post
        This usually means your polling interval is too fast. Try to reduce the polling interval, and try to set a short (250ms) delay between each address poll in the "Advanced" settings of your gateway. Once it settles, you can start to reduce the delays to optimise your reads.
        Thanks for getting back to me.... Below is my settings. Do I need even more time?

        Thanks Jay
        Attached Files

        Comment


          #5
          No, that's more than enough. Can you try enabling just one register and seeing if that will read. Then let's increase it from there and see where we go?


          Sent from my iPhone using Tapatalk
          Author of Highpeak Plugins | SMS-Gateway Plugin | Blue Iris Plugin | Paradox (Beta) Plugin | Modbus Plugin | Yamaha Plugin

          Comment


            #6
            Originally posted by beerygaz View Post
            No, that's more than enough. Can you try enabling just one register and seeing if that will read. Then let's increase it from there and see where we go?


            Sent from my iPhone using Tapatalk
            Thanks again for the reply


            I have tried that with the same results, after a few hours it stops updating - disable and re enable the plug in its good for a few more hours.

            Jay

            Comment


              #7
              Sorry Jay. I thought you were the OP. You seem to have hijacked his thread with a different issue.

              I don't think your issue is a timing one.

              Can you enable debug logging and log to file and then run the plugin until you see updates stop happening and then send me the modbus log file in the \Logs folder.

              Perhaps I can see why updates stop happening.


              Sent from my iPhone using Tapatalk
              Author of Highpeak Plugins | SMS-Gateway Plugin | Blue Iris Plugin | Paradox (Beta) Plugin | Modbus Plugin | Yamaha Plugin

              Comment


                #8
                My apologies if I have "Hi Jacked" The thread title caught my eye as I am trying to figure this out. - Should I start a new thread?


                Yes I will get you the log file.


                Thanks for the quick response.


                Jay

                Comment


                  #9
                  Please Jay. It will help future users with your issue and help me keep track of problems outstanding too.


                  Sent from my iPhone using Tapatalk