Announcement
Collapse
No announcement yet.
WDTC-20 How to test with volt meter?
Collapse
X
-
Here is a site that has HVAC wiring info with definitions: http://wiki.xtronics.com/index.php/T...als_and_wiring
And here's a link to the diagram on that site: http://wiki.xtronics.com/index.php/Image:Thermostat.gif
Unfortunately, there are no standards when it comes to furnace and A/C wiring color codes, but in general, the Red wire (terminal R) is generally considered the 24vac "hot" and the Black wire (terminal B) is 24vac "common." The 'stat works by connecting 24vac hot to the other terminals to call for heat, A/C and/or fan. These command inputs are generally relays and the other sied of each relay is connected to 24vac common inside the furnace and a/c units.
Where 24vac hot get a little messy is when both the furnace and a/c units each supply their own 24vac hot. This is where the RH and RC terminals come in as they 24vac hot.
So, to test that you really do have 24vac being supplied to your 'stat, measure the AC voltage between terminals RH and C for the furnace and and then measure between RC and C for the A/C unit. If either or both of these are near 24vac (20-28) then you should be good. If not, the 24vac common line may not be connected back at your furnace or A/C unit.Best regards,
-Mark-
If you're not out on the edge, you're taking up too much room!
Interested in 3D maps? Check out my company site: Solid Terrain Modeling
-
RockLobster,
The wdtc-20 has a jumper, I forget which one, but is marked if you have both Heat and AC with separate power supplies I think you remove it.
Then If you want to run the stat with an separate ac supply you would put one connection on the C and the other on the RH. Your heat wires from the furnace would go to RH and W.
Tech support at WD told me that this isolates the thermostat supply from the individual supplies.
Stuart
Comment
-
pwhite8314
Did you get to the bottom of this?
I had all sorts of issues with it consuming batteries, it turned out that the problem was not the wiring, but the fact that the hot wire contact was not making contact with the stat, so it was running on batteries the whole time. This was because the wall it was mounted on was a bit rough, so the left side of the plate was a tiny bit deformed, causing the pin to be slightly further away from the stat when it's mounted on the plate. By 'slightly' I mean something like 0.01mm, but, due to the crappy design of the backplate, that was enough to screw things up.
I've now done away with the backplate completely and hardwired the wired direct into the stat through a custom plate. I like the WDC-20, but it's design is very poor.
Comment
-
OK, my HVAC guy is here and we found the problem... hopefully this will do it. Using a voltmeter, the Common to RH is only giving 15-16v. The Common to RC is giving the full 24v, but I've learned that the WDTC-20 needs 24v from the *heating system*.
So the HVAC guy is going to run a jumper from the cooling system to the heating system, we'll then test to ensure we're getting 24v between C and RH.
Which reminds me... is there any way to tell when the 'stat is running off of batteries? It sure would be nice to know one way or the other before he leaves!
Thanks again everyone...
Comment
-
Originally posted by RockLobster View PostOK, my HVAC guy is here and we found the problem... hopefully this will do it. Using a voltmeter, the Common to RH is only giving 15-16v. The Common to RC is giving the full 24v, but I've learned that the WDTC-20 needs 24v from the *heating system*.
So the HVAC guy is going to run a jumper from the cooling system to the heating system, we'll then test to ensure we're getting 24v between C and RH.
Which reminds me... is there any way to tell when the 'stat is running off of batteries? It sure would be nice to know one way or the other before he leaves!
Thanks again everyone...
Try removing the batteries completely - if the display works, then it is working from the 24v AC supply.HS4Pro on a Raspberry Pi4
54 Z-Wave Nodes / 21 Zigbee Devices / 108 Events / 767 Devices
Plugins: Z-Wave / Zigbee Plus / EasyTrigger / AK Weather / OMNI
HSTouch Clients: 1 Android
Comment
-
pwhite8314
Try removing the batteries completely - if the display works, then it is working from the 24v AC supply.
Comment
Comment