    Incomplete polling

    Spud,

    Just installed my two last thermostat and I'm getting incomplete polls for them :

    Unit #9 : Control mode is not reporting

    Unit #10 : 3 out 9 values seemed to have polled one time and are not being updated since then. See attached capture and it is 17:01 right now.

    What I tried :
    - Restart HS and PI
    - Rebuild network on Neviweb.
    - Delete and recreate #10 in HS
    - Changing the poll time from 1 to 2

    Note 1: All units are interacting normally in Neviweb.
    Note 2: If I change the setpoint via HS, the value is going thru.

    Strange to see this with the 10th unit?

    Running V3.0.0.8

    Let me know if you want me to check something in particular.
    Attached Files

    #2
    could you post some debug logs?

    thanks

    Comment


      #3
      Attached (3) minutes of pools.

      Unit #10 is ID 103665
      Attached Files

      Comment


        #4
        in your logs I saw some "buffer full" error messages, meaning the plugin sends too many requests at once. I added some "sleep" functions between request to avoid that. I never ran into this problem because I don't have that many Sinope devices, so please test version 3.0.0.11 attached. Thanks
        Attached Files

        Comment


          #5
          Spud,

          Thanks for the prompt fix that I could not test before this AM.

          Your induced sleep delay in 3.0.0.11 seems to have fix the issue as the missing values are now coming in, without seing any "buffer full" log entries. Your explanation about your test bed being smaller then my set-up is coherent with what was I was observing.

          Again many thanks for the fast update.